The onsite guide is not for comercial installations.

So im taking a different footing here, the ring circuit design in the onsite guide is for the purpose of a domestic single phase system amongst other prerequisites. So the installed ring is the design of someone? You need to prove it meets the requiremnts of BS7671. Specifically 433.1.103 plus the other general requirements.

Cheers

I thought we were talking about the ring circuit design in bs7671 not the idiots guide?
 
Read the whole thread, the answer is in post 2, appendix 15.

Dave, thats not a ring circuit design, its sets out the special regulation 433.1.103, that asisde its down to the deisgner to meet all the other general requirements.

Cheers
 
Dave, thats not a ring circuit design, its sets out the special regulation 433.1.103, that asisde its down to the deisgner to meet all the other general requirements.

Cheers

I've not got the book in front of me but I thought that was where there is a full page illustration of the standard ring final circuit with spurs etc clearly illustrated.
 
I've not got the book in front of me but I thought that was where there is a full page illustration of the standard ring final circuit with spurs etc clearly illustrated.

Yes it shows you a typical arrangement, no design spec. The standard circuits in the onsite guide have prerequsites set out, if these are not met then you need to design the circuit and show compliance.

Cheers
 
Also that little diagram is based on the ring being wired in 2.5.
In this case as initially explained the ring is wired in 4mm with a proposed 4mm spur
 
i wouldn't just guess its 4mm based on vd.

we were laughing at the way overspeced supplies on some jobs.

they were told your not allowed to use anything smaller than 4mm XD

it was for little smoke damper boxes controlling an individual smoke damper.

another personal favorite was a 70mm supply to a panel that only had 50a isolator
 
Also that little diagram is based on the ring being wired in 2.5.
In this case as initially explained the ring is wired in 4mm with a proposed 4mm spur

Without further information we have to assume a worst case scenario that 4mm has been used due to de-rating factors making the ccc of 2.5mm too low for a ring. So without further information we cannot assume that the 4mm when de-rated has only got the ccc of the 2.5 in the standard circuit.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom

Thread Information

Title
Can i spur more then once with bigger cable?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
48

Advert

Thread statistics

Created
tomodo,
Last reply from
davesparks,
Replies
48
Views
4,356

Advert