Discuss Can you calculate ring final conductors if you have a measured R1 + R2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

bcwright

Hello there everyone, I've dead tested some ring mains on a job recently but unfortunately I didn't do my measured end to ends. The circuits only have two spurs on each.

I have my R1 + R2's, it was wired in 4mm T and E so the earth is obviously 1.5mm.

For example, if one circuit measured 0.33 ohms, is there a calculation to work out r1, rn and r2.

Many thanks in advance.
 
Hum... be nice.

How can you dead test a RFC and NOT do the end to end readings?

EDIT: Its not as if the end to end isn't important!
 
Last edited by a moderator:
Being kind...

If - and this is a big if - you have:

- all the readings (R1+R2) from all sockets on the RFC (not just the highest) and
- knowledge of the lengths and cross sectional area of cable between all sockets (and back to the DB)

... then you can, for most circumstances, be pretty confident of r1 and r2, and will be able to confirm from your calculations whether the ring is continuous or not. (unless there are two faults that cause equal and opposite effects).

However, knowing R1+R2, there is no way on earth you can give a value for rn. And if the neutral is not continuous, this is a dangerous fault.
 
Hello there everyone, I've dead tested some ring mains on a job recently but unfortunately I didn't do my measured end to ends. The circuits only have two spurs on each.

I have my R1 + R2's, it was wired in 4mm T and E so the earth is obviously 1.5mm.

For example, if one circuit measured 0.33 ohms, is there a calculation to work out r1, rn and r2.

Many thanks in advance.
Word of advice, ask a mod to close this thread.
 
Hello there everyone, I've dead tested some ring mains on a job recently but unfortunately I didn't do my measured end to ends. The circuits only have two spurs on each.

I have my R1 + R2's, it was wired in 4mm T and E so the earth is obviously 1.5mm.

For example, if one circuit measured 0.33 ohms, is there a calculation to work out r1, rn and r2.

Many thanks in advance.

What's fortune got to do with it ? Apart from ... unfortunately you'll have to return to the job and do it properly.
 
@ the OP. Go back and carry out the full test procedures.

I'm closing this thread now. Any questions please PM the Staff or myself directly.
 

Reply to Can you calculate ring final conductors if you have a measured R1 + R2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock