Nothing to do with dogs,

A customer has got a manky old CU in a cupboard in his kitchen. I'm doing the wiring in the kitchen and he wants me to put the new CU in a cupboard above the worktop.

He doesn't want any trunking and to get the tails up to the cupboard I would have to chase the tails in:eek:

Is this do-able? Would I have to mechanically protect them against nails etc?

I know it's not ideal, but I can't think of any other way I can do it.

Thoughts?
 
Where is the meter in relation and what route are the tails currently taking, personally i wouldn't chase them in, how about installing a fused isolator and then running in a split concentric cable?
 
Where is the meter in relation and what route are the tails currently taking, personally i wouldn't chase them in, how about installing a fused isolator and then running in a split concentric cable?

Meter is on the other side of the wall mounted outside. tails currently run through the wall and into kitchen.

They're also 16mm at the mo with 100A cutout!

Whatever I use to get up to this cupboard has got to go in the wall.

Is split con the best way to go? Why split con over swa?

I've never had a go with split con, what's it like to terminate compared to swa?

apologies for all the questions!
 
Last edited by a moderator:
just seen another thread on the IEE forum an a bloke on there was going to chase them in and cover them in 3mm steel plate as protection.

If I used SWA would that do for "protection"?
 
I thought that neither of those methods could be taken to be protection against nails, screws etc.

i know the whole "protection" thing is a grey area but I'm just thinking about after I'm long gone, I don't want someone (daft homeowner) putting a screw into a 25mm tail!
 
well technically if it's going straight up it's in a safe zone. Plus if the person puts a nail through the earthed capping it will only short between the capping and the tail, there is only so far you can go. You would have to be going some to put a nail through 32mm galv conduit :D
 
Last edited by a moderator:
. You would have to be going some to put a nail through 32mm galv conduit :D

indeed:)


Will I be able to squeeze 2x25mm tails and a 16mm earth into 32mm galv?

It's in a kitchen so I think the safe zones will need either mechanical or RCD protection if they're going in the walls. (I await correction)

I'm leaning towards 25mm tails chased in and 3mm plate for protection.
 
It may get a bit tight but it should go. Have a look at 522.6.6 gives some pretty good pointers.
 
Dare I say the dreaded word some cringe at

Cavity :)
 
It may get a bit tight but it should go. Have a look at 522.6.6 gives some pretty good pointers.


Hmmm, yes, seems according to 522.6.6, if they're enclosed in earthed conduit or earthed trunking that would appear to comply.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
chasing tails
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Thread Tags

Advert

Thread statistics

Created
Benny_Boy,
Last reply from
Benny_Boy,
Replies
16
Views
2,832

Advert