Can anyone shed any light on some strange really low readings on a ring final circuit I've just 2nd fixed including replacing some legs as the IR was bad in places on old cabling before.
Thought it could be my MFT batteries going and therefore giving possibility of silly results but upon getting home I tested a part used drum of 1.5mm T & E and got good results ! I'm new to doing my own testing so am a bit baffled. Drum I tested I estimate at 60-70 metres or so left on maybe a touch more but can't find my OSG to look up the resistance per metre of 1.5 Twin, readings were L-E 1.43 ohms, N-E 1.49 ohms, and L-N 1.15 ohms which looked reasonable whereas on the ring r1 was 0.00 ohms, rn also 0.00 ohms and r2 0.16 ohms !! Thinking something silly has been overlooked here ? R1 + R2 tested at almost certainly furthest point too and had 0.00 ohms there too ?? Have two sockets wired as spurs too and no difference there either ! I expected higher resistance readings on them.
Half hoping that due to being up best part of week these nights with poorly 5 yr old my brain has overlooked a fundamental mess up !
Hey Dave, I actually forgot to post that I read exactly that and also batteries on the decline on the Fluke giving spurious readings and the batteries are low'ish showing on self test at 7.2V and should be 9V when new batteries in it. But by testing the drum of 1.5mm I thought if batteries I'd still get 0.00 or near, but I actually got a reading as above that looked o.k.
I did null leads using the zero function and via deducting the read resistance myself to make sure, Croc clips together and by using the little fluke zero adapter that was in the case ! ( piece of pricey metal !! lol )
and usually once zeroed / nulled it's retained as zero but this time / a few times it read 0.07 ohms say, then after showed random 0.3 ohms on display etc.. or such like but when continuity tested was reading leads at zero ! so seemed o.k. so tried zero / null button again and get a different reading each time on leads and then instead of 0.0 on screen would show random still results ! weird that. It's a 1653B in case that makes any odds and has been brilliant and calibrated 2 months ago.
Have you tried it with another set of leads.
I am not familiar with fluke , but leads can be worky tickets.
I'm sorry I must not of read post properly , I did not see were you had done IR testing .
If leads were faulty it would show through the ranges.
No apology required buddy, I never mentioned that I had done IR tests or similar, only listed the r1 rn etc.. at first, just thought even though basic stuff that I may have made a huge fowl up somehow.
As I said , I am not familiar with MFT's. I use Megger separates. I had a similar problem with a faulty lead; and a bad contact on the batteries.
As it has already been mentioned, it sounds like faulty leads. I had a similar problem last year with mine and a new set sorted the problem.
My leads were intermittently faulty, which I discovered when I compared them to my mate's leads (same make leads) on my tester
Reply to Concerning R1 + R2 and r1,rn,r2 ring final results ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...