My practical for Inspection & Testing is coming up towards the end of the month and im a little unsure about how to test the main equipotential bonding for continuity.

My tutor told me that one end of the Main Bonding conductor has to be removed from the MET in order to remove any parallel paths.

The part im unsure on is exactly where to place the probes for the continuity test. Any assistance or guidance much appreciated...

Thanks for reading,

Jabbajaws... :confused:
 
Hi there.

Basically as follows -

1. Safely isolate the supply
2. Disconnect one end of the conductor, preferably the end at the consumer unit.
3. (Null out test leads) or ( record and remember to subtract from end result)
4. Connect one test lead to the conductor at the CU
5. Connect the other test lead to the metal work of which the conductor you are testing, (ensure any painted metal work has been scratched off, to make a solid connection). By not connecting it to the clamp this will prove the clamp has a good connection to the pipework
6. Test using a low resistance ohm-meter.

The result will give the total resistance of the conductor (remembering to subtract the test lead resistance, if not previously nulled out)

7. Re connect bonding conductor
8. Job done.

Hope this helps.:)
 
Hi, Sounds like you need to buy a copy of the NICEIC testing book.

A great guide for the tool box.

I have just finished my 2330 and had a few points i needed to brush up on and I found it very usefull.

Cheers

Dave
 

Reply to Continuity (Main Equipotential Bonding) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
272
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
629

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock