To do a R1+R2 test you connect the Line and Cpc together and test at the furthest point.

But on the test sheet I have there is also a box for just an R2 test aswell, how do you correctly do just an R2 test?
 
the R2 column is there because sometimes it may be impracticable to measure R1+R2 due perhaps to reasons of safety.
 
To do a R1+R2 test you connect the Line and Cpc together and test at the furthest point.

But on the test sheet I have there is also a box for just an R2 test aswell, how do you correctly do just an R2 test?

A small point, but you take a reading at all outlets and record the highest (which should be at the extremity of the circuit).

Regards
 
i thought the R2 test was for old circuits that dont have cpc's in them??? finding a few old lighting circuits with no earths in them here in cornwall lol

I don't understand what you're saying here. R2 is the resistance of the CPC. How can you do an "R2 test" if there's no CPC?

Or are you just having a laugh?
 

Reply to Continuity testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
881
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
510
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
673
Hello everyone, I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead...
Replies
1
Views
931
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
674

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock