Discuss Cooker and Hob help in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
Afternoon all

Been asked to connect up cooker and Hob. Guy only has one 32amp cooker supply in 6mm. Has isolation point and connection point at low level

Spec for cooker is 2.4KW but has 13 amp plug fitted. So from that i read it as this cannot be connected up to 6mm connection point and has to have fused spur taken of kitchen supply and low level socket provided.
Hob is 16 amp and says requires hardwiring to dedicated circuit. Why would this be the case wouldn't it be adequate again to spur of kitchen supply and provide a connection point for this? Any advice appreciated
 
Cheers. Combined though they overrate the 32 amp breaker for cooker circuit don't they?. I Could spur out from low level connection point for cooker but where do I get my supply for hob. Sorry edit no this can't be case as only 16amp for hob although ratings for ring are 2.2kw 2kw 2kw and 2kw. I still can't see where I should fuse hob load though
 
Hi - the 16A hob doesn't need an additional fuse. If it was connected to the connection unit with a 3 core flex of 2.5mm (say) then the conductors can’t be overloaded and the cpc is the same size as the rest of the 6mm twin and earth radial circuit.

If I’ve understood correctly, the total load is 13+16=29A so that’s well ok too.
 
Hi - the 16A hob doesn't need an additional fuse. If it was connected to the connection unit with a 3 core flex of 2.5mm (say) then the conductors can’t be overloaded and the cpc is the same size as the rest of the 6mm twin and earth radial circuit.

If I’ve understood correctly, the total load is 13+16=29A so that’s well ok too.


Hob and oven are fixed load,
You can take both off the existing cooker feed if you want.

Cheers guys really appreciated will make sure get 2.5 heat resistant flex so will have 2.5 c.p.c
 
fit a cooker outlet for the hob and a socket for the oven, both from the existing 6mm 32A circuit. use one of these.
1575817380759.png
 

Reply to Cooker and Hob help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
743
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
656
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
801

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock