I "nearly" understand the diversity calc, first 10a plus 30% of remainder, I just can not get my head around how 6mm cable and a 40a mcb is adequate for this size of cooker when if you installed a 10.5kw shower it wouldn't be.
 
Last edited by a moderator:
I "nearly" understand the diversity calc, first 10a plus 30% of remainder, I just can not get my head around how 6mm cable and a 40a mcb is adequate for this size of cooker when if you installed a 10.5kw shower it wouldn't be.

No diversity on shower as capable of taking full load, chances of cooker seeing full load of 17kw highly unlikley thats why diversity comes in.
 
So if the cooker in question has all functions running on full steam, it would still not reach 17.1kw. Why dont the manufacturers test the cooker on full power and indicate the exact figure, then the circuit could be deisgned and installed with the extra added confusion.
 
So if the cooker in question has all functions running on full steam, it would still not reach 17.1kw. Why dont the manufacturers test the cooker on full power and indicate the exact figure, then the circuit could be deisgned and installed with the extra added confusion.

Not quite, the cooker is capable of outputting 17kw on full steam but the chances of someone turning the whole lot on full at once is slim and even then the thermostats are going to be switching the elements on/off intermitantley to reach temp. So although everything is turned on by operator it's the stats that call for power so once upto temp they knock off.
 
Not quite, the cooker is capable of outputting 17kw on full steam but the chances of someone turning the whole lot on full at once is slim and even then the thermostats are going to be switching the elements on/off intermitantley to reach temp. So although everything is turned on by operator it's the stats that call for power so once upto temp they knock off.

lol!! ...Not quite again!! ...the 17KW is the connected load, the fact is it CAN'T all be switched on at one time as there are elements within the oven section that can't be ultilised at the same time, a good example is the grill element, it can't be used during oven operation. then there are multiple oven elements in modern ovens, some can be utilised at the same time others can't.

But i agree that manufacturers should in this day and age state maximum KW loading, rather than the connected KW load.... As a 17KW cooker isn't really 17KW, it's more like a 15 or 15.5KW cooker....
 
lol!! ...Not quite again!! ...the 17KW is the connected load, the fact is it CAN'T all be switched on at one time as there are elements within the oven section that can't be ultilised at the same time, a good example is the grill element, it can't be used during oven operation. then there are multiple oven elements in modern ovens, some can be utilised at the same time others can't.

But i agree that manufacturers should in this day and age state maximum KW loading, rather than the connected KW load.... As a 17KW cooker isn't really 17KW, it's more like a 15 or 15.5KW cooker....

Why bother ?
 
Last edited by a moderator:
i "nearly" understand the diversity calc, first 10a plus 30% of remainder, i just can not get my head around how 6mm cable and a 40a mcb is adequate for this size of cooker when if you installed a 10.5kw shower it wouldn't be.
thats because when you install a shower there is no ,,,, diversity allowed.....but in a cooker there is....that why see....lol...
 
But i agree that manufacturers should in this day and age state maximum KW loading, rather than the connected KW load.... As a 17KW cooker isn't really 17KW, it's more like a 15 or 15.5KW cooker....

e54... If you apply the basics of the cooker diversity of first 10a plus 30% of remainder, have i got this right...??

17.1kw = 74.35a
10a + 30% of 64.35a = 29.3a

So, the circuit you install must be designed for 29.3a = 6.7kw ??
 
6mm clipped direct, 40A MCB. that's my opinion, for what it's worth
 
But i agree that manufacturers should in this day and age state maximum KW loading, rather than the connected KW load.... As a 17KW cooker isn't really 17KW, it's more like a 15 or 15.5KW cooker....

e54... If you apply the basics of the cooker diversity of first 10a plus 30% of remainder, have i got this right...??

17.1kw = 74.35a
10a + 30% of 64.35a = 29.3a

So, the circuit you install must be designed for 29.3a = 6.7kw ??

it's worked for 60 odd years. no reason to think any different today. best thing is in the proof of the pudding, as they say. switch everything on and clamp meter it. initial current might be a little bit over, but bet it settles down to no more than 30(ish) amps.
 

Reply to Cooker cable sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
838
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
617
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
268
Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if...
Replies
1
Views
621
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
551

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock