Welshsparky

Got a CU change coming early next week, 16mm tails supplying consumer unit, protected by a 60 amp fuse at the main head, is it a requirement to upgrade to 25mm regardless of the fuse size?
 
16 mm tails will take 60 A no problem.

I don't know which requirement you mean unless you are looking at the OSG which I believe have a 100A main fuse which would require 25 mm tails!
 
Im just confirming to be honest! i was handed an EICR by the customer from his previous electrician who stated they must be upgraded, was wondering if id missed something!
 
previous spark need moola for holiday abroad, ergo, customer needs unnecessary work doing.
 
As the others have said, 25mm tails not required for 60A supply. I think the confusion comes from the OSG which works on the premise that new supplies will be 100A, hence 25mm needed.
 
I try to upgrade tails if possible even on a 60a supply - (I do have a 100m roll of 25mm I must add that I acquired somewhere that needs using up)
I just cost it into the job now - I believe it to be a betterments although not a necessity.
 
If I was replacing the tails for some reason I'd probably go for 25mm, but if there was no compelling reason to swap the tails, I'd leave them well alone!
 
As the others have said this myth stems from the OSGs one-size fits all solution.
Thats most likely the biggest problem with most of the comments and questions on the site, people are using the OSG as a replacement for the regs and missing the point of the last word in the title of the book.
Yes there are regulations quoted in there but with the little pictures its taken as gospel that this is how it should be.
Perhaps it would be better to call it the dummies guide but then we still have the 'G' word in there.
 
As far as I'm concerned the "mandatory" 25mm tails applies to rewires and new builds.....


If the OSG covered all situations it wouldn't fit in your tool bag!
 

Reply to CU Tails in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
402
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
824
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
696
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock