Discuss CU Tails in the Electricians' Talk area at ElectriciansForums.net
W
Welshsparky
Got a CU change coming early next week, 16mm tails supplying consumer unit, protected by a 60 amp fuse at the main head, is it a requirement to upgrade to 25mm regardless of the fuse size?
16 mm tails will take 60 A no problem.
I don't know which requirement you mean unless you are looking at the OSG which I believe have a 100A main fuse which would require 25 mm tails!
Im just confirming to be honest! i was handed an EICR by the customer from his previous electrician who stated they must be upgraded, was wondering if id missed something!
previous spark need moola for holiday abroad, ergo, customer needs unnecessary work doing.
As the others have said, 25mm tails not required for 60A supply. I think the confusion comes from the OSG which works on the premise that new supplies will be 100A, hence 25mm needed.
I try to upgrade tails if possible even on a 60a supply - (I do have a 100m roll of 25mm I must add that I acquired somewhere that needs using up)
I just cost it into the job now - I believe it to be a betterments although not a necessity.
If I was replacing the tails for some reason I'd probably go for 25mm, but if there was no compelling reason to swap the tails, I'd leave them well alone!
Reply to CU Tails in the Electricians' Talk area at ElectriciansForums.net
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...