Anyone tell me what Ive done wrong here lads?

Wired up a starter today, 2 DOL contactors with 415V coils fed through two Telemec Motor Overload units sitting side by side in an enclosure.

Wired up from the Red phase through a Stop and Start button back through A2 with hold on contact 13/14 used and A1 onto Blue phase. No O/L as its thru the Motor O/L unit above the contactor. Press the start and 'bang' blew the main fuses. it was like a dead short. frustrated as its just a simple circuit.

Checked all the wiring and its fine, looked for diagrams and checked and its fine. Where have I gone wrong???What have I done wrong here????
 
Was the motor connected or were you just testing the DOL starter on its own?

Sounds like now would be a good time to dust off the tester.
 
Wasnt connected to the motors Marvo, i checked all the wiring as per drawings and its correct but still blows the fuses as in a short. I cannot fathom out a stupid wee fault like this. Phasing is correct, all control wiring is correct. I am at my wits end. I cant help thinking its something further back down the line but we use the supply elesewhere on other starter panels with no hassles.
 
start with the basics. power off ohm meter across A!-A2. see if there's a short across the coil/s. then progress from there.
 
Done that mate, the two coils are fine. Its weird because according to any diagram Ive looked at, the wiring Ive done is exactly as stated, and by the way, Ive done this work for years which makes it even worse for me!!!!, I cannot figure out why it blows fuses, I had to walk away from it earlier, I was so hacked off.
 
what's on the load side of the contactor/s?
 
Hmmm, I thought of a stupid question and I'm going to ask it anyway. Are you sure the starter arrangement with 2 x contactors isn't a star/delta starter with the link wires still across one of the contactors?.

With your post count you shouldn't have any problems if you want to attach a photo or two to give us a better idea of your setup.
 
Its two dol contactors side by side lads controlling two motors, they are seperate from each other. wiring is the same for both, and both come thru motor protection breakers from Telemec. All im doing is trying to energise the two contactors both with 415V coils thru a start and stop button, easy peasy or so you would think. Its so easy Im stumped !!!!
 
bet it's so simple that a 2nd look will spot it right away.
 
Its two dol contactors side by side lads controlling two motors, they are seperate from each other. wiring is the same for both, and both come thru motor protection breakers from Telemec. All im doing is trying to energise the two contactors both with 415V coils thru a start and stop button, easy peasy or so you would think. Its so easy Im stumped !!!!

Check both A2's on each coil are fed/linked from the same phase for starters.
Then make sure each control circuit is on the same phase too and ends up at A1.
Sounds like it's crossed somewhere and giving you a short.............I am on my umpteenth bevvy btw:).

Don't try this at home kid's lol
 
Post a photograph or two.

Out of interest is this a reversing starter or two drives?

If the fuses blow when the contactor closes it points to the motor terminal side. Had the fault been on the control the MCB's would have tripped.
 
Last edited by a moderator:
Thanks for that wee gem of advice Paul, this is why I rarely come onto this forum for info !!!

Most of the folk are very genuine and helpful while other 'experts' go out their way to make statements like they are know it all. Why make a statement like that? If you want to help, then please help.

If Ive done something wrong, then point out why and where I can get the info so I understand why I went wrong. Is that not easier for you???
 
FWIW, if it was me i would check the coil voltage first as it wont be the first time..
second i would double check the wiring by "belling", i.e. ignoring any wire numbers just in case a bit of brain fade when numbering (wouldn't be the first time).
Then i would check the resistance of the coil to make sure someone was not having a laugh and marked up a 24V coil as 400V ..:))
 
Right .... the main issue with simple problems is they sometimes elude you so what i suggest is you take a picture of the set-up im sure it will be clear for us to head you in the correct direction...

If you have not loads connected to contactors and it shorts when hitting start button then it points to a simple wiring issue in your control circuit either through oversight or lack of understanding and you seem clearly creating a short when energising the coil... it may be down to confusion here .... pic of the wiring and contactor will help with indicators of any wires going out of view.
 
Thanks for that wee gem of advice Paul, this is why I rarely come onto this forum for info !!!

Most of the folk are very genuine and helpful while other 'experts' go out their way to make statements like they are know it all. Why make a statement like that? If you want to help, then please help.

If Ive done something wrong, then point out why and where I can get the info so I understand why I went wrong. Is that not easier for you???

Although you have not suggested you have exported your control circuit he raises a good point if you have ... if your start stop are remote and you are controlling the coil with 400v then you will be in a possible contravention of regulations ... this is not part of BS7671 and if your don't know what regs it falls within then you shouldn't even be touching this. You shouldn't take offense at such a post as it states a good point if you are offended then reply that you are fully aware and his concerns are not the case or we will obviously question your competence in such an area.
 
I know you can become blind to an obvious mistake if you look at it for too long but your meter doesn't! Surely a continuity test across pairs of (dead) supply lines will tell you what is being shorted and when, if you check both by pressing the start button and by pushing the contactor in by hand. Then you will know if it is in the main circuit or the control. If that doesn't narrow it down enough.... post pics!
 
i would disconnect link from A1 to blue phase and operate start button with power on to see if it takes out supply.this should start to narrow it down.
 
i would disconnect link from A1 to blue phase and operate start button with power on to see if it takes out supply.this should start to narrow it down.

No no no!!!
You're proposing blowing out a box of fuses until you find the fault! :smilielol5:
I think I'd go with Lucien's advice.
 
operate start button with power on to see if it takes out supply.

There seems to be a lot of enthusiasm around for faultfinding with live tests. Inverter drive lacking torque - probably necessary. DOL starter blowing fuses - probably not! Should be able to spot the problem in 3 minutes with an AVO...
 
I still have my old avo...............probs well over 50yr old now cos it was old when I 'acquired' it :)

mmmmmmmm................e-bay or antiques roadshow is the question?
 
Sorted out lads, turned out to be a fault on the control transformer. 415v to 115/24.

Thanks for all the help lads, took a wee bit of head scratching and looking at it too long then realised where the fault was.
 
I still have my old avo...............probs well over 50yr old now cos it was old when I 'acquired' it :)

mmmmmmmm................e-bay or antiques roadshow is the question?

I still have an AVO EFLI meter. I've never had one problem with it, so simple and reliable and tough!...unlike the megger which is in for repair AGAIN!. I don't rate them at all any more.
 
Sorted out lads, turned out to be a fault on the control transformer. 415v to 115/24.

Thanks for all the help lads, took a wee bit of head scratching and looking at it too long then realised where the fault was.

Im totally lost now you explained fully how the set-up was wired ...2 contactors, overloads, and control 400v on A1 / A2 via the start stop buttons....
You also said when energised it went bang when the start button was pressed.... ???

Where the hell did the transformer come from and you say its for control 115/24 ..... i though we were on 400v control and surely the 'control' transformer is energised on power up thus the fuses will have blown on power up not after the start button has been hit....

Have i totally missed something here what you just described has nothing to do with your thread opening post so we really had little chance of nailing the problem for you.
 
Last edited:
Sorted out lads, turned out to be a fault on the control transformer. 415v to 115/24.

Thanks for all the help lads, took a wee bit of head scratching and looking at it too long then realised where the fault was.

What exactly is your definition of 'fault on the control transformer' ?
Wiring it up wrong isn't a fault mate :)

- - - Updated - - -

Sorted out lads, turned out to be a fault on the control transformer. 415v to 115/24.

Thanks for all the help lads, took a wee bit of head scratching and looking at it too long then realised where the fault was.

What exactly is your definition of 'fault on the control transformer' ?
Wiring it up wrong isn't a fault mate :)

Wow............double slap in the face soz for that !!
 
Me thinks it was a schoolboy error with a cover story ...totally contradicted his original opening post.... we all have these moments me included but its takes the mick when the solution don't relate to any other post he's wrote .... ..so either he's covering up or just wasted our time with lack of or misguided infomation.
 
Just saw this, perhaps the fault on the control transformer was that it was still on the wholesaler's shelf until post #16

Yes very funny Marvo, your photoshop work is OK up to a point but the BANANA plugs seem to be missing from the test leads (no, I am not suggesting you invest any more time :)
 

Reply to DOL starter 415V coil in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
499
Hi there, I got a call to a job, table saw (wood) tripping C/B straight away. 4kW motor on Star Delta Starter. So I get to the job, after some...
Replies
2
Views
3K
Hi all From the outset I'm not in an electrician. I am posting here because I'm thinking the subject matter is quite specific and will prob...
Replies
43
Views
7K
Aside from every screwdriver in the universe, I wonder what the most creative mis-use of a tool you have encountered is. I'm sure this example can...
Replies
37
Views
4K
Hi all I would like a bit of advice to do with a DOL starter ill be fitting. Basically I'm replacing an old water damaged crabtree DOL starter...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock