G

GBDamo

I have been asked to look into a random tripping RCD.

The installation is quite simple, now only only four circuits,

None RCD protected side has only the lights and a redundant 16A MCB 2.5mm radial for which no accessory could be found, possibly disconnected outside lights but the circuit was still live, this has been disconnected and put in connectors in the CU.

RCD side has a 16A MCB 2.5 radial with only one double socket outlet, a 32A MCB ring doing the majority of the sockets (possibly with a ring off the ring but that's another story), a 20A 2.5mm radial doing living room sockets and finally a 40A MCB 6mm redundant circuit serving a removed shower.

All IRs pass although the 20A radial and 32A ring both had low readings at 2-3MOhms. All other tests pass comfortably.

However the 40A ex-shower circuit still had the Neutral and CPC terminated in the CU, the other end could not be located, probably cut off and plastered in the bathroom wall.

I have disconnected the the Neutral and CPC for the ex-shower and made them safe in terminal blocks in the CU.

After 4 days there have been no more random tripping whilst I've tidied up some loose ends I'm concerned that I haven't really found the fault.

Could a Neutral and CPC buried in a damp wall like this cause an RCD to trip?

Any thoughts welcomed.
 
I think you are correct ...
To clarify the electric shower was replaced by a bar mixer before my friend bought the house but the circuit for the shower is still in place. That is it runs from the CU to a location unknown, assumed to be cut off and plastered into the bathroom wall.

The live had been disconnected in the CU but the Neutral and CPC had not.

This tripping has been on and off for the three years they have had the house.
 
^^ sometimes these things happen.

I had been investigating random tripping in a very big 3 story house a couple of years ago. Dual RCD board

In the end I recommended the customer changed to a rcbo board ....
Which was implemented.

A few months later the 3rd story socket circuit started to trip.... Eventually I found a cable disappearing down a wall behind the shower room below. I disconnected the spur and it's never tripped again.

Very trying to deal with.
 
Its nice to find a screw through a cable or some such that you can point to and say "that's it" but it's not always the case.

Just don't want to be getting a free breakfast under false pretenses.
 
Just to ensure it it doesn't become and remain live due to coming into contact with another live conductor?

bed time now, thanks for the assistance all.
Well, perhaps, although the more likely scenario is someone reconnecting it in the DB. Hopefully if all cores are earthed they may stop and think. (No guarantee there though, I'm afraid. Stupid never fails to surprise...)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Domestic favour, tripping RCD and redundant circuits
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
GBDamo,
Last reply from
sparksfly,
Replies
26
Views
3,980

Advert

Back
Top