Hi,

Friend of mine wants a new feed for double oven, however now it's a double oven and a hob.

Double oven is 7.4kw and hob is 7.4.

My Calc applying diversity is

7400/230 = 32a

32+32 = 64a (14720w)

First 10a+30% of remainder +5a for socket so

10a+16.2a+5a= 31.2a

My questions are, is diversity applied to individual items or items combined? So hob and oven seperate or together? (As you can see iv done it together)

Next question, is it advisable to run 2 seperate circuits for this or could it run on 1 circuit (with carefully selected fuse/cable)
 
On site guide suggests one circuit for 2 supplies can be used for a design current of upto 50 amps.
As long as the cooker control switch is within 2 meters of Each appliance
 
Ok so in this case that's fine.

However if I can't apply diversity to say the hob it may be over 50amps
 
IMG_2925.JPG
 
Yes it is so my calculations are valid?

As for isolation I plan to use a 2 DP switch with a plug as I thought it would be good to have individual control between oven and hob
 
Just dotted these calc down. Look right?



IMG_1184.JPG
 
Just dotted these calc down. Look right?



View attachment 37388
CCC is not 38 amps as this is for 6mm 3 phase supplies buried try 46 amps, tho you would need to apply a 0.9 cc correction factor as the tables give the ambient temp as 20 degrees Reference method D and not 30 degrees as the other reference methods are .this correction factor corrects for overload but need not be applied to a cable underground if overload is omitted say for a fixed load.
is the cable buried?
 
Last edited by a moderator:
Yeh it's buried, so the correction factor need not be applied?

Ah yeh I see about the CCC. It's 46A ref method D.
 
Yeh it's buried, so the correction factor need not be applied?

Ah yeh I see about the CCC. It's 46A ref method D.
Needs to be applied and there also depth to consider, ambient temperature of ground etc.
You could argue that overload isn't a factor as the load is calculated using diversity but I never personally omit overload protection for cookers.
Others might I don't.

The cable CSA you've selected 6 mm looks fine.
Only you know how it's being installed so be wary if you need to apply any more derating factors which might affect your cable CSA choice
 
  • Agree
Reactions: telectrix

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
~
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Double oven/hob- single circuit or double
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
gazdkw82,
Last reply from
Ian1981,
Replies
9
Views
148

Advert