Discuss Earth Fault Loop Impedence question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
K
kshah86
hello, i got this qustion and would like someone to show me the working out of it please.
the measured value of loop impedance for a circuit is 0.83 ohms. if the temperature at the time of the test was 20c and the cable is 70c (factor1.2), what is the correct value. ze = 0.4 ohms
your circuit resistance is multiplied bt 1.2 to allow for temperature. there fore, you would deduct the Ze from the Zs and adjust the remaining figure accordingly.
You cannot apply the correction factor to the measured value of loop impedance (Zs) as this includes the external loop impedance which is not subject to the 70c correction factor. So you need to subtract that from your Zs to give you your R1+R2 then apply the correction factor (1.2) then add the Ze back on.
The formula is:
= Ze + F(R1+R2)
Using your figures:
0.4 + 1.2 x 0.43 = 0.4 + 0.516 =0.916.
i dont understand this question surely the measured zs is the correct value
it is. the question is badly worded. normally, we correct the max. value allowed to allow for temperature rise.
Reply to Earth Fault Loop Impedence question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Hi, I am currently studying to become an electrician and keep seeing this question (normally different values) and I am not sure how to work this...