Just want to see what people’s thoughts are on this, doing an EICR today. Testing the lighting circuit, 1 cable at every accessory which means joint box somewhere. Hall light is a pendant wired in 2 core PVC cable, no earth at it. Tested at kitchen light and got a reading, then tested at living room light and although cpcs were connected at light and switch I wasn’t getting a reading. I’ve marked this down as further investigating on the lighting circuit, client not too happy that the floorboards are going to have to come up from upstairs lol! Would you pass the circuit in these circumstances? Feel a bit uneasy about it
 
it's a C3 if all fittings are plastic. C2 if metal. your approach is correct to investigate and rectify. serves 'em right for gatting a cheap cowboy in the first place.
 
It isn't a case of passing the circuit, cpcs are present with no continuity.
 
i would be torn between C3 and C2 even with all plastic fittings. still got metal back boxes on switches with metal faceplate screws. so more inclined to C2.
 
It isn't a case of passing the circuit, cpcs are present with no continuity.
Dodgy connections at joint box definitely would be my guess, don’t want to lift floorboards but needs must
 
Dodgy connections at joint box definitely would be my guess, don’t want to lift floorboards but needs must
If you are doing an EICR state the facts remedial consequences are for later.
 
If there's no cpc present, the wire pre dates the requirement for a cpc to be present, and there's no exposed metalwork present, then C3.
If there's a cpc present, with no continuity to the main earth terminal, then it's C2, even if there is no exposed metalwork present.
Chances are that it's modifications done in the '70s, when twin cable was no longer available, and the cpc was just ignored, but it could just be a break in the wiring somewhere, giving the possibility of a disconnected cpc coming into contact with a live terminal, or a fault to the cpc at one point exporting that fault to any other floating cpcs.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Glasgow
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
EICR no CPC at light
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
Welsh_sparky_21,
Last reply from
brianmoooore,
Replies
7
Views
4,315

Advert