Check your connections at shower and isolator. It's possibly a bad connection or a cable not stripped back properly and tightened down onto the insulation. Have you tested the circuit R1 + R2 etc?
If RCD/MCB is ok water pressure is ok connections ok only thing really to do is get an electrician in to test properly it may be that the fault with the old shower wasnt a fault at all but you may have problems elsewhere that is causing both showers to misbehave.
The purge pin is only on their digital remote triton showers sorry . It may be a water pressure problem. If in doubt call in someone or call triton and ask their technical department.
Thanks for you assistance i did call trition and they asked me to check the voltage, did not seem to helpful not sure if it is water pressure as the presure light is not on
Thanks again
Did they let you know what the call out fee is? it may be more cost effective to get someone in to confirm it's the shower then call triton in for free?
I had this on a shower the over week, it turned out to be a dodgy pull cord. check the voltage on the incoming and outgoing side of the pull cord and that will show you mate.
Hi,
I would say check the connections at the isolator, in case the supply and load are not the right way round or supply live in correctly, but neutral supply in the load side ????