Hi Guys went to look at a friends house he has just bought, at some point the CU has been moved from just behind DNO board to 6 meters away using 10mm T&E as a temp feed loose cliped inside. The Outside cabinet has the meter head in with 25mm tails going to an isolater switch and the temp feed from that.

I would like to make this right for him so was looking to use SWA on the out side of the building 6 meters then into the back of the new CU both the cabinet and the CU are on the same wall just 6 Meters away

Firstly what size SWA do I need 25mm ?

or would I be better to use normal 25mm meter tails inside plastic conduit insted of swa ?

Any advise would be good I am Part P Quallified but done very little work like this and have just been recovering from a big operation I had 6 months ago so still not very active at the mo..

Thanks

Chas
 
SWA for me. 25mm 3 core. gland into galv adaptable box below CU and feed tails through. ditto at isolator.
 
What's the earthing system?
 
Or use 16.0mm Armoured as you'll probably need to fuse down for the supplier as its more than a few metres. 16 will take well over 80 Amps. Clipped or on tray/in free air.

or in a bath of liquid nitrogen.
 
  • Like
Reactions: 1 person
Should have said it is TNC-S earthing system, looking at calcs I think 16mm swa from a sw fused isolator at DNO end and terminate into a steel box and tails to cu ,,, or would it be safe to go streight into cu with swa,, which does not seam right or safe to me??

Thanks

Chas
 
If TN-C-S, then just a fused isolator at the supply end will be OK. You need to assess whether an 80A fuse and 16mm² SWA will be OK, which it will be in the majority of domestic situations, or whether you need to fit a 100A fuse and 25mm² cable. The size of the existing supplier's fuse may be a guide.

I wouldn't worry about trying to get any discrimination between the supplier's fuse and the additional one.

If the CU is metal, then obviously you can terminate directly into that. If plastic, terminate into a galv box positioned against the CU and just run the cores and bedding into the CU.
 
Thanks for all your help guys I am cool with that now so can get on and sort it for him

Cheers
Chas
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
External Meter tails Help
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Power Ball,
Last reply from
Power Ball,
Replies
7
Views
2,628

Advert