Hi Guys went to look at a friends house he has just bought, at some point the CU has been moved from just behind DNO board to 6 meters away using 10mm T&E as a temp feed loose cliped inside. The Outside cabinet has the meter head in with 25mm tails going to an isolater switch and the temp feed from that.

I would like to make this right for him so was looking to use SWA on the out side of the building 6 meters then into the back of the new CU both the cabinet and the CU are on the same wall just 6 Meters away

Firstly what size SWA do I need 25mm ?

or would I be better to use normal 25mm meter tails inside plastic conduit insted of swa ?

Any advise would be good I am Part P Quallified but done very little work like this and have just been recovering from a big operation I had 6 months ago so still not very active at the mo..

Thanks

Chas
 
SWA for me. 25mm 3 core. gland into galv adaptable box below CU and feed tails through. ditto at isolator.
 
Or use 16.0mm Armoured as you'll probably need to fuse down for the supplier as its more than a few metres. 16 will take well over 80 Amps. Clipped or on tray/in free air.

or in a bath of liquid nitrogen.
 
Should have said it is TNC-S earthing system, looking at calcs I think 16mm swa from a sw fused isolator at DNO end and terminate into a steel box and tails to cu ,,, or would it be safe to go streight into cu with swa,, which does not seam right or safe to me??

Thanks

Chas
 
If TN-C-S, then just a fused isolator at the supply end will be OK. You need to assess whether an 80A fuse and 16mm² SWA will be OK, which it will be in the majority of domestic situations, or whether you need to fit a 100A fuse and 25mm² cable. The size of the existing supplier's fuse may be a guide.

I wouldn't worry about trying to get any discrimination between the supplier's fuse and the additional one.

If the CU is metal, then obviously you can terminate directly into that. If plastic, terminate into a galv box positioned against the CU and just run the cores and bedding into the CU.
 

Reply to External Meter tails Help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
393
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
283
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
NICEIC Certification Scheme Mounting EV charger on external meter cabinet
Customer wants me to mount his EV charger on the back of an external, plastic meter cabinet. The cabinet is a new plastic one at the other side of...
Replies
1
Views
621

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock