Ring testing isn't solely at the CU. r1+rn and r1+r2 should also be tested at each point, this would identify any spurs and faults etc.
Besides, a single double socket has the potential to draw 26amps,
I don't think that's right. r1,rn,r2 at the CU would only tell the ring is continuous, but it wouldn't tell you if someone had spurred off it. The R1+R2 at the CU, I'm less sure about, but I still don't think it will tell you someone has spurred off the ring. But this is besides the point: is a socket circuit protected by a 20amp safer that a 32amp?
Not surprised at allring testing at each socket? now that I did not know.
And (R1+Rn) - although this isn't recorded in the Schedule of Test Results it still forms part of ring final circuit continuity testing.If r1, r2, rn , R1+R2 reading are all in order then there womt be a break or spur on the circuit
Not as entertaining as this thread, I still reckon he is a wind up merchant, no one is this dopey.OP's kept you all amused this afternoon. I think you've all been had.
You could direct your enthusiasm and waste your time with the guy wanting to power up his mancave.
ring testing at each socket? now that I did not know.