Discuss Fault with ring main in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
I was testing a consumer unit before upgrading to current standards. (Old re wireable fuses) when testing one of the ring mains continuity i found 38v on the cpc with that circuit disconnected. After carrying out end to end tests on Line and neutral which came back fine. I found the voltage dissapared when I removed the fuse for the lighting circuit?
Any advice on what this would be?

I also have continuity between neutral and line on a leg but haven't had time to investigate further, i e splitting the ring.
Thanks in advance
 
I was testing a consumer unit before upgrading to current standards. (Old re wireable fuses) when testing one of the ring mains continuity i found 38v on the cpc with that circuit disconnected. After carrying out end to end tests on Line and neutral which came back fine. I found the voltage dissapared when I removed the fuse for the lighting circuit?
Any advice on what this would be?
If measured with a typical digital multimeter probably just capacitive coupling (the so called "phantom voltages"). DMM often have around 10M impedance so it only take 3.8uA to read 38V, getting that by two cable running side-by-side for a reasonable distance is easy.

I also have continuity between neutral and line on a leg but haven't had time to investigate further, i e splitting the ring.
L-N short? Surly it would have been blowing fuses before you got there?

If measured with a IR tester though it probably means < 0.01M ohm and that could be anything still connected with even modest load, such as filament lamp, motor in fridge, etc.
 
If measured with a typical digital multimeter probably just capacitive coupling (the so called "phantom voltages"). DMM often have around 10M impedance so it only take 3.8uA to read 38V, getting that by two cable running side-by-side for a reasonable distance is easy.


L-N short? Surly it would have been blowing fuses before you got there?

If measured with a IR tester though it probably means < 0.01M ohm and that could be anything still connected with even modest load, such as filament lamp, motor in fridge, etc.
Sorry not line and neutral - continuity between neutral and earth with the ring pain disconnected at the board
 
Sorry not line and neutral - continuity between neutral and earth with the ring pain disconnected at the board
OK, more likely and going to trip RCDs!

Probably a lack of grommet in some back box, or cable crushed up, so hopefully you can find it with a bit of systematic searching.

If it is a very low R fault you might be able to get some idea of roughly how far by measuring N1-E1 and N2-E2 and the ratio of resistance ought to put you roughly at the ratio of distances to where it is shorted.
 
OK, more likely and going to trip RCDs!

Probably a lack of grommet in some back box, or cable crushed up, so hopefully you can find it with a bit of systematic searching.

If it is a very low R fault you might be able to get some idea of roughly how far by measuring N1-E1 and N2-E2 and the ratio of resistance ought to put you roughly at the ratio of distances to where it is shorted.
Yeah looks like I'll have to do that, what was the most puzzling is that this voltage disappeared when I removed the fuse for one of the lighting circuit.
 
I've had this very problem just recently, only found it when fitting an RCBO board and both the lighting and [sole] ring RCBOs tripped everytime the downstairs hall light was switched on..... Can't access the borrowed neutral so had to come up with a temporary solution until boards can be lifted etc - can you guess what I've done for the time being ?🙂
 
Well there's only 1 lighting circuit as well , and the ground floor hall light comes on with the landing light, that only has the usual loops and 1 switch wire. So I reckon the linking was a more recent thing and the bottom light has the switched live tapped off the L2 of the three core from the landing 2 way with neutral from a ring link -all above the ceiling with the room above totally loaded with clutter. So for now I've spurred the lighting from the ring RCBO through a fused spur with 5a fuse right next to the CU. 🙄
 
Last edited:
I was testing a consumer unit before upgrading to current standards. (Old re wireable fuses) when testing one of the ring mains continuity i found 38v on the cpc with that circuit disconnected. After carrying out end to end tests on Line and neutral which came back fine. I found the voltage dissapared when I removed the fuse for the lighting circuit?
Any advice on what this would be?

I also have continuity between neutral and line on a leg but haven't had time to investigate further, i e splitting the ring.
Thanks in advance
L-n load could be anything, even a neon on a spur. Are you new to testing?
 

Reply to Fault with ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
480
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
272
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock