Can someone please explain why we have to cross conductors from legs of a ring to perform figure of 8 test (r1+r2 or rn+r1) and why we can't just link those conductors from the same leg as it would also make a loop... Would I be right in thinking that you would get a more even reading across both conductors when connected in figure of 8. Rather than the way I said as it would measure a much shorter distance. And would give inaccurate readings?
 
cross connecting creates a big loop where all the sockets are the same distance apart, step 2, 3 prove polarity
 
not only that, but by cross connecting, all your outlets should give the same value for R1+R2, unless there;s a spur off the rfc.
 
As tel said, easy way to locate spurs and loose connections.
If you don't connect them to opposites they will go up as you go along the ring then back down.
Like your loop readings will.
 
As tel said, easy way to locate spurs and loose connections.
If you don't connect them to opposites they will go up as you go along the ring then back down.
Like your loop readings will.

yes beacuse the disatnces are not the same
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
figure of 8 test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
Monkeyblaine,
Last reply from
morph,
Replies
7
Views
4,092

Advert