The spd needs a live neutral and earth, normally connected after the mainswitch in a Cu, but there’s no reason it can’t be connected before.

you’ve already put one in? Then it’ll protect both if both main switches are on
 
The main issue with SPD is the cable length.

What they are trying to stop are surges in the microsecond range and as a result all of the power is spread up in to the 100kHz+ region and so cable inductance dominates over resistance in almost all cases.

So if you have the SPD on the CU such that the cable length from supply L tap point to SPD and back to N tap point & E to MET is less than 1m (but ideally less than 0.5m) the SPD will protect loads off both CU.
 
Single phase or 3 phase?
[automerge]1601235786[/automerge]
The spd needs a live neutral and earth, normally connected after the mainswitch in a Cu, but there’s no reason it can’t be connected before.

you’ve already put one in? Then it’ll protect both if both main switches are on
As @pc1966 says there is a length of you need to be under for it to be fully effective.
 

Reply to Fitting off spd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Client needs an SPD fitting but no room in c/u or adjacent. Best bet looks like a parallel connection into the tail blocks in the meter cabinet...
Replies
3
Views
328
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
873
Hi got a 8 panel solar system on bungalow, changing the board to 18th edition spd board Solar feed is chased into wall so will this need a type B...
Replies
4
Views
282
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
954
Hi everyone, Got a job converting commercial property into 4 flats, 2 up 2 down all with electric meters on the outside on ground floor, SWA to...
Replies
0
Views
640

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock