Has anyone fitted an SPD to a schneider standalone AFDD DB.

Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways​


This board only takes AFDDs so there is no where for the SPD MCB to go. There is a DIN rail next to the main switch. The SPD comes with a separate enclosure.

Acti 9 surge arrester kit 40kA withdrawable 3P+N​

Has anyone had this issue and if so how did you do it. I thought about installing the MCB on the DIN rail then going to the SPD in the separate enclosure. The issue with this is that the incoming tails are 35mm and I would need to feed the MCB in 35mm, so wouldn't have room in the main switch terminals for 2 x 35mm. Any ideas???
 
This board only takes AFDDs so there is no where for the SPD MCB to go. There is a DIN rail next to the main switch. The SPD comes with a separate enclosure.
A quick search shows there is an SPD option next to the incoming switch. Do you need it MCB protected? Many of the bigger SPD are safe to supply OCPD of 125A or 160A so it might be covered by the sub-main feed.
The issue with this is that the incoming tails are 35mm and I would need to feed the MCB in 35mm, so wouldn't have room in the main switch terminals for 2 x 35mm. Any ideas???
You don't need 35mm to the SPD, it is typically OK for 6mm L/N & 16mm CPC so providing they are mechanically protected (double sheathed, inside DB or DIN box bolted to that, less then 3m length though for SPD should be 0.25m ideally or 0.5m max) so don't need supply protection they are protected by the load MCB.

But again, does the SPD need additional protection?
 
That SPD kit looks like it is intended for use with a standard Acti9 board, it's got the neutral link to go onto the busbar stack etc.

You should speak to Schneider technical but I'm fairly sure it's the wrong SPD kit.
 

Reply to Standalone AFDD board requiring SPD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Replies
10
Views
1K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
I've been asked to install Schneider AFDD's into a single phase board. I'm to supply the board with RCBO's and AFDD's. I've purchased the new...
Replies
3
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hello, I have a Clipsal consumer unit with two "ways" unused and blanked off and potentially a third available as the Proteus Geyer B16 MCB is...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock