The difference between the Fluke and the Metrel is only how it displays correct and incorrect sequence. Nether meter can 'know' which two lines are swapped if the sequence is incorrect, because it doesn't 'know' which is which in the first place. If the Metrel displays incorrect rotation by showing two specific lines swapped, that's merely symbolic. Swapping any two lines will correct the sequence, although there's only a 1 in 3 chance that they will then all be labelled the same as they are at the incomer.

OTOH I would expect it to correctly flag up a single line fault, as it merely has to detect the lack of voltage, although some MFTs will still show rotation either correct or incorrect even when the voltage symmetry is badly adrift, e.g. with one line probe connected to neutral.
 
I would agree,that spending a few hours of an evening,having a play,would be time well spent.
I always do this,unless the test instrument or equipment,just won't fit in the lounge....

I remember doing this with one of my Megger mft's,and getting familiar with the alarm limits,polarity reversal,and button functions. It just makes a device more useful,if you can occasionally make good use,of it's capabilities.....which you have paid good money,for :)

How many times,have folk on here,described a particular function,on a MFT,to have it's long-term owner,say "I never knew it did that...";)
 
Fun fact, most of the liverpool area runs in the wrong direction from the rest of the country.

Happened because of a mistake made years ago when we were transitioning from DC. It' s been the wrong way for so long now correcting it is impossible. The DNO are just aware of it an work around it.
Greater Belfast is the same. It is different to the rest of NI.
 
Fun fact, most of the liverpool area runs in the wrong direction from the rest of the country.

Happened because of a mistake made years ago when we were transitioning from DC. It' s been the wrong way for so long now correcting it is impossible. The DNO are just aware of it an work around it.
there's a reason for that, Rob. it's because the Mersey flows east to west, unlike the Thames which flows west to nowhere.
 

Reply to Fluke Phase Rotation Testing help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
429
Been called to help a friend who can't get anyone to look at his car lift until next week and it's stopping him from working. I said I'd have a...
Replies
14
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
662

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock