Hi all I fitted 3 5FT fluorecent fittings in a garage, I removed 3 batten fitting so it was a straight swap, problem is when customer switches on the lights the RCD in the house trips. Should these lights go on the non RCD side
 
Hi all I fitted 3 5FT fluorecent fittings in a garage, I removed 3 batten fitting so it was a straight swap, problem is when customer switches on the lights the RCD in the house trips. Should these lights go on the non RCD side

If you're asking that, should you have fitted the lights in the first place?

Could you have trapped a cable in one of the fittings?

Did you do a N-E IR test?
 
Hi all I fitted 3 5FT fluorecent fittings in a garage, I removed 3 batten fitting so it was a straight swap, problem is when customer switches on the lights the RCD in the house trips. Should these lights go on the non RCD side

I have to agree with IQ Electrical, this is very basic and if you areasking this then you probably should have done this work. If these lights are tripping the RCD then there is a fault. Either in the wiring or with 1 or more of the lights. As previosly stated you need to IR test the circuit. split the circuit and test at different points.
 
Thanks for your reply to my question on fluorescent lights tripping RCD. Further to this the customer has informed me the lights were not switched on when the RCD tripped. They were a replacement for 3 battens on existing wiring controlled from a switched fused spur connected on the RCD side of the DB. I know this type of switch isolate both lines when off. So how does this cause the RCD to trip, if these lights are to blame.
 
is it a double pole FCU? most are only single pole. also, it's possible a faulty RCD. or as previously stated , a fault on the work you have done. only way is to IR the circuit and go from there.
 
Last edited:

Reply to Fluorescent lights tripping RCD in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Sorry no photos, but I’ll explain best I can. Turn on the switch, I’m not getting any light. Apparently a new fitting. Description…. A white...
Replies
3
Views
265
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
411

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock