Two points to mention here, as its a removable gland plate then the integrity of the earthing relies on the self tapping screws holding the plate down to the panel (although in your example there are fly tail already connected that may give a better route to earth), had it been a solid construct panel and adequate measures had been taken to give good contact like serrated washers then it may have been acceptable, (not the case in the example pictures). My second point is regarding taking earth loop readings, you are sending a low DC current through this quesstionable connection, this will show you a given reading that the earth path exists or not but it cannot be relied on totally to make a judgement call, normally in fault <1000 amps will flow and if it passes through a weak spot as above could be then that can create high resistance or breakdown which may cause the OCPD to operate out of permitted trip times, this could lead to damage to the cabling of the circuit and the integrity of isulation.

These boards probably just require a serrated washer on the inside and a common fly lead looped to the bonding terminal, I see no reason to power down and stop production as these boards are designed with finger protection and isolated stubbs, so unless you have other reasons to need to power down the full board then I cannot see why a professional who is aware of the dangers within this board cannot leave them energised while the work is done, this is where the stupidity of H&S red tape tramples on common sense and actual risk, use a risk assessment and if you don't see any immediate concern like exposed or damaged conductors that would increase the risk then just plan it as a routine job.
 
Two points to mention here, as its a removable gland plate then the integrity of the earthing relies on the self tapping screws holding the plate down to the panel (although in your example there are fly tail already connected that may give a better route to earth), had it been a solid construct panel and adequate measures had been taken to give good contact like serrated washers then it may have been acceptable, (not the case in the example pictures). My second point is regarding taking earth loop readings, you are sending a low DC current through this quesstionable connection, this will show you a given reading that the earth path exists or not but it cannot be relied on totally to make a judgement call, normally in fault <1000 amps will flow and if it passes through a weak spot as above could be then that can create high resistance or breakdown which may cause the OCPD to operate out of permitted trip times, this could lead to damage to the cabling of the circuit and the integrity of isulation.

These boards probably just require a serrated washer on the inside and a common fly lead looped to the bonding terminal, I see no reason to power down and stop production as these boards are designed with finger protection and isolated stubbs, so unless you have other reasons to need to power down the full board then I cannot see why a professional who is aware of the dangers within this board cannot leave them energised while the work is done, this is where the stupidity of H&S red tape tramples on common sense and actual risk, use a risk assessment and if you don't see any immediate concern like exposed or damaged conductors that would increase the risk then just plan it as a routine job.

Reason mention power down was the report states for corrective actions ' To isolate supply, fit fly leads to each SWA. I also believed the common earth to be adequate. The only thing I saw wrong with this DB and the others similar is that no washers. however, after a phone call with the inspector he hadn't even noticed that.
I have 300 reports with unsatisfactory condition. All C2's. Many of which I'd class as C3's. example C2 for no evidence of RCD testing although there's 5 years of annual and functional reports to hand and many more in archive.
C2 for no chart etc.
These as 2391 & 2394/2395 qualified myself would class as C3.
Having a huge bill come through for remedial works as a total rather than broken down also for immediate repairs required.
 
Reason mention power down was the report states for corrective actions ' To isolate supply, fit fly leads to each SWA. I also believed the common earth to be adequate. The only thing I saw wrong with this DB and the others similar is that no washers. however, after a phone call with the inspector he hadn't even noticed that.
I have 300 reports with unsatisfactory condition. All C2's. Many of which I'd class as C3's. example C2 for no evidence of RCD testing although there's 5 years of annual and functional reports to hand and many more in archive.
C2 for no chart etc.
These as 2391 & 2394/2395 qualified myself would class as C3.
Having a huge bill come through for remedial works as a total rather than broken down also for immediate repairs required.

The serrated washer would be for a situe' where a fly lead wasn't necessary but you needed a reliable contact, I suggested still putting one on as it would stop the nut from loosening with time if its subject to any form of vibration etc, this could equally be achieved with a spring loaded washer or if your lack these then doubling the nuts up can be a solution, the spring loaded would be your best approach using a second nut as this means you wouldnt be disconnecting the earth path on a live circuit, I would issue your own risk assessment and submit it to the powers who be that these corrective measures can be done without power down lthough a small risk of accidentally knocking a mcb off does exist when fitting or removing the cover, although re-itterate that it is a small risk unless you note the MCB's are poorly fitted and don't fully line up with the lid cutouts.
 
I know this thread is a bit old. However we are pontificating on the exact same problem. Only in this case there are 40 office metal clad DB to do and 40 clients to disrupt. I cant quite get my head around what we are trying to do here. In our case the earth is supplied in the three core L-N-E. The armour is not the earth supply. So we think no problem then ? But working on lights above the suspended ceiling, I have received a shock between the grid and the earth in a unit in two separate buildings. Measuring the voltage received it is 120v. We bonded the metal box to earth and the voltage disappeared, in one of the buildings. However in the other it turns out it was due to a neutral being connected to earth at one lighting point in a chain of 18 external emergency lights. We are still puzzling over this thinking perhaps a loose neutral?
 
Hi V - sounds like it - otherwise you are running with a neutral 120v above gnd? You have found one implementation error, there may be more. The Inspector in me says test the installation. Better than another surprise.
On the earlier DW #24 post (tin hat on) ... Wouldn't we have to power down to release the cable from switchgear to slip the extra nut or washer on? Still no coffee here so I may have lost the plot :)
 
I would have thought that good workmanship applies when terminating glands, conduit etc to a metal enclosure, what happened to cleaning the paint and making a nice shiny surface to fix to. In my day we used to clean the ends of conduit couplers, and both inside and outside of metal enclosures, guess they don't teach that on these Mickey Mouse courses. Do them up tight with a fancy bush spanner, sorry I'm ranting again.
 
would have thought that good workmanship applies when terminating glands, to quote Pete
These boxes were put in 20 years ago, not sure on the designers/installers thinking leaving out fly leads on this one. Maybe they did clean of paint and fix to bare metal.
 
Good workmanship to my mind, does not entail doing something that is unnecessary.
To my mind in many cases SWA is an over specification for the purpose the cable is intended to provide.
Drilling holes and installing fly leads is often just work for work's sake.
 

Reply to Fly Leads For Swa On A Metal Clad Db in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
815
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
Replies
28
Views
3K
I have a metal Hager sub CU, 10 way RCBO, installed in 2018 in an accessible attic space, this sub-CU being fed from another unit close to the...
Replies
11
Views
6K
I've got a bunch of old single phase BS88 1970s fuseboards in the communal areas of a converted building. All the wiring is MICC and it's buried...
Replies
9
Views
1K
Hi all, Hope you are all well and all is good! I am installing a sub board being fed by a 80A SP+N Metal Switch Fuse at source, this is feeding...
Replies
9
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock