good evening,

brain has gone walkabouts tonight

can i put a 13amp switch fused spur from a spur i.e

sockets ring main - spur- switched spur?
the load is only a t.v nothing heavy

alternative would put the swicth fuse in before the spur, then spur off the spur but like to avoid as decorated house
its all rcd etc.
thanks
 
if its fcu first then you can have as many sockets as youd like. if the spur is feeding a socket then that has to be end of the line. regardless of load theres potential for overloading the cable.
 
  • Like
Reactions: 1 person
Putting the fcu after the spur would be just the same as adding another socket so a no no, can it not go by the side of the spur and go to that first then you can add sockets til your hearts content, or the fuse blows, one of the two, or by the side of the socket its spurred from
 
Remove existing 2G socket, replace back box with dual box, install S FCU on ring, then single and as may accessories as you like there after.
 
  • Like
Reactions: 2 people
agree, however in theory theres no problem IMO, but we have to adhere to the men at the IEE in suits don't we?
 
Of course there's a problem.
There's a possiblity that the conductors may become overloaded, if more than one accessory is wired to an unfused spur.
 
Hmm yes In theory I suppose, well Okay I suppose 27 amps could be exceeded on the leg in a house
 
Last edited by a moderator:
Ok I did wonder,
fused spur before the initial spur it is then.

I can't tiger Paul as the spur is a socket and there would be no overload protection
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
fused spur from a spur
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
dim_bulb,
Last reply from
MDJ,
Replies
9
Views
1,886

Advert