Looking for a little help on submission of G 59 application, local DNO has said application is good to go but they need the following:
A clear narrative description of the scheme that describesthe scheme operation during mains healthy, loss of mains, return of mains and paralleling (where applicable).
using 3x17000 to inverters.
anyone done this before, also any help on wording would be great. Submitted one before but never been asked for this.

Many thanks
 
Hello Renewgreen I have submitted a G59 generator b4, August 2011... at my time it was enough sending back proof of compliance with
G59-2 especially in regards to disconnection time and "purity" of energy generated... meaning confirmation of inverter set to generate electricity at grid frequency below 50.5 Hz. Plus usual wiring diagrams, site plant drawing and schematics...
 
Hello Renewgreen I have submitted a G59 generator b4, August 2011... at my time it was enough sending back proof of compliance with
G59-2 especially in regards to disconnection time and "purity" of energy generated... meaning confirmation of inverter set to generate electricity at grid frequency below 50.5 Hz. Plus usual wiring diagrams, site plant drawing and schematics...

Hi Solar Midlands, done all of above but they still want this description of operation. I argued that the description is all within the inverter G59 certificate. I guess they don't want too look through to find info. Any thoughts on how to word scheme operation?

Mank thanks
 

Reply to G59 description in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
579
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
380
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hi all, I was reading about what can happen if the neutral on a PME system is lost at some point before the cutout and I have a few questions that...
Replies
67
Views
14K
In addition to the 4 main, well known competent persons schemes (NICEIC, ELECSA, NAPIT and STROMA), there is apparently another, lesser known...
Replies
18
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock