Discuss G59 description in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

R

renewgreen

Looking for a little help on submission of G 59 application, local DNO has said application is good to go but they need the following:
A clear narrative description of the scheme that describesthe scheme operation during mains healthy, loss of mains, return of mains and paralleling (where applicable).
using 3x17000 to inverters.
anyone done this before, also any help on wording would be great. Submitted one before but never been asked for this.

Many thanks
 
Hello Renewgreen I have submitted a G59 generator b4, August 2011... at my time it was enough sending back proof of compliance with
G59-2 especially in regards to disconnection time and "purity" of energy generated... meaning confirmation of inverter set to generate electricity at grid frequency below 50.5 Hz. Plus usual wiring diagrams, site plant drawing and schematics...
 
Hello Renewgreen I have submitted a G59 generator b4, August 2011... at my time it was enough sending back proof of compliance with
G59-2 especially in regards to disconnection time and "purity" of energy generated... meaning confirmation of inverter set to generate electricity at grid frequency below 50.5 Hz. Plus usual wiring diagrams, site plant drawing and schematics...

Hi Solar Midlands, done all of above but they still want this description of operation. I argued that the description is all within the inverter G59 certificate. I guess they don't want too look through to find info. Any thoughts on how to word scheme operation?

Mank thanks
 

Reply to G59 description in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all I had my PV/Battery setup installed in May and since then all my excess PV is just fed back to the grid for free. When I initially tried...
Replies
1
Views
2K
Are you looking for a career in the South West, with endless opportunities for development? Do you want a hands-on role where your skills and...
Replies
0
Views
1K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
TLDR: is there a legal requirement to have a landlords supply to power an L2 alarm system? Mornin'. Non-electrician, under the cosh from an iffy...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock