I've been in both situations (both years ago)- surprised to not get a jolt standing on soil when it had just rained after I messed up isolating an outside light, and surprised to get a jolt on a wooden step ladder on ary concrete floor.
While we all understandably conclude that standing "outside" is very dangerous and standing "inside" is very safe, it is, nt always, as clearcut as that. "outside" earth will be very dry and very unconductive if you have a few weeks of good dry summer days. Add on to that someone wearing good shoes and sockets (not after a hard day's work and perspiration) and you will certainly have a high resistance path. On the "inside" as mentioned by other posters, if you have an older home with a concrete floor with no damp coarse you will certainly feel a tingle and perhaps something more. I recently "felt" 27 volts due to a faulty shower while wearing shoes and socks and my feeling afterwards was "Well I can understand the homeowners panicky phonecall now" as he received the same shock with water flowing down around his feet.
I must also say that regardless of any situation I encountered there was never any mystery to the shock felt. It could all be explained by Ohms law.
 
4) What, if anything, is in place to protect against these sorts of dangerous situations occurring?
I, ve just read the detail regarding that very, very sad case of the 7 year old electrocuted in a pub garden due to a seriously underspec electrical intallation.
Its sobering to consider that the exact same problem could occur with the same fatal consequences in a PME installation considered up to spec.
 
I, ve just read the detail regarding that very, very sad case of the 7 year old electrocuted in a pub garden due to a seriously underspec electrical intallation.
Its sobering to consider that the exact same problem could occur with the same fatal consequences in a PME installation considered up to spec.

Quite! although rare, it seems strange too me so many people accept that risk !
 
I, ve just read the detail regarding that very, very sad case of the 7 year old electrocuted in a pub garden due to a seriously underspec electrical intallation.
Its sobering to consider that the exact same problem could occur with the same fatal consequences in a PME installation considered up to spec.
Very tragic case. Unless I'm missing something I guess you mean with broken upstream Neutral as per this thread or exposure to live parts (as was case in the water filled light you referred to).

Also sobering, this isn't exactly a new debate - I spotted the following discussion elsewhere several years ago which is rather poignant:
1615193743260.png
 
Very tragic case. Unless I'm missing something I guess you mean with broken upstream Neutral as per this thread or exposure to live parts (as was case in the water filled light you referred to).

Also sobering, this isn't exactly a new debate - I spotted the following discussion elsewhere several years ago which is rather poignant:
View attachment 65376

Exsactly whey my outside lights are SELV or double insulated, they are in easy reach and one of them is likely to be touched
 
Also sobering, this isn't exactly a new debate -
Correct. It's an old debate. However, far from being yesterday's news it has the potential to become very current with one single high profile incident. The example below (outside light) would probably have constituted the vast bulk of "at risk" metalwork under open PEN , 25 years ago.
Today the level of "at risk" exposed metal parts outside the home has changed enormously (electric gates, heat pumps to mention but a few). Add to that the DSO, s approach of employing largely TNC-S for new installs plus converting existing TNS cables to TNC-S when repairs are required.The electrical landscape is starting to look very different and with that change the potential for open PEN issues can only increase.
 
Correct. It's an old debate. However, far from being yesterday's news it has the potential to become very current with one single high profile incident. The example below (outside light) would probably have constituted the vast bulk of "at risk" metalwork under open PEN , 25 years ago.
Today the level of "at risk" exposed metal parts outside the home has changed enormously (electric gates, heat pumps to mention but a few). Add to that the DSO, s approach of employing largely TNC-S for new installs plus converting existing TNS cables to TNC-S when repairs are required.The electrical landscape is starting to look very different and with that change the potential for open PEN issues can only increase.
The conversion of old TNS to TNCS in the street and the head staying the same inside the property I feel is a concern as a spark could install something (hot tub, heat pump, etc etc) outside believing the loss of PEN conductor risk is not an issue due to the fact it is TNS, him being unaware it is really now TNCS
 
The conversion of old TNS to TNCS in the street and the head staying the same inside the property I feel is a concern as a spark could install something (hot tub, heat pump, etc etc) outside believing the loss of PEN conductor risk is not an issue due to the fact it is TNS, him being unaware it is really now TNCS
I suspect that an experienced spark will likely test the supply and be pretty sure what he is dealing (or perhaps ring the DSO) but, yea to make a major change in the supply system by converting a TNS to a TNC-S and not leaving a very clearly marked label or"record " of it behind for the homeowner (and future electrician) is I feel very, very poor practice.
 
how can you test the supply to find out earthing type or maybe we just assume a ZE less than 0.35 is most likely some variation of TNC-S.
I don't think there is any easy test.

If the PFC & PSCC are very similar then all it tells you is the earth and neutrals have similar impedances, it is not explicitly telling you if they are common fairly close to the property in TN-C-S style.

With the power off at your installation looking the the (supply side) N to E voltage would give to an idea of how much current imbalance & impedance was present on any PEN cable, but that is also likely to pick up some volts from inductive coupling from other loads in the network.

However, if that voltage is very low, say less then 0.1V or so, you could probably do a resistance measurement N-E to get an idea of how far away any common point is if you have an idea of the type of cable feeding you (e.g. 16mm split concentric or whatever) so you know R per unit length.
 
how can you test the supply to find out earthing type or maybe we just assume a ZE less than 0.35 is most likely some variation of TNC-S.
"pc1966" sums that up nicely. What I would add (or ask) is how could making such a fundamental change in the supply network go un noted? Afterall an electrician would feel duty bound to inform a homeowner that replacing a wooden shed with a metal one might necessitate a TT...ing of the electrical supply to it for safety reasons (I, m trying to think in UK terms here and may stand to be corrected).
How then could a service provider change the nature of the system supplying a whole street without considering the potential knock on effects for the various homeowners who carried out installation under a previous supply system? Am I making any sense here?
 
What I would add (or ask) is how could making such a fundamental change in the supply network go un noted?
I suspect the move to TN-C-S was started many years ago when (a) most folk did not have significant outdoor power requirements like EV and hot-tubs, and (b) when the cables going in were nice and new and joint failures of the outer PEN of aluminium waveform cables was not an expected thing.

Fast-forward 30 odd years and here we are.
  • Proper TN-S would be the safest/best system, but costs the DNO that earth extra conductor.
  • Going TT like much of the EU avoids the DNO expense and the open-PEN risk. But in turn it pushes the extra cost on the home owner as they need an incoming RCD (unusual over two decades ago before the regs demanded them on most circuits) and an earth rod, which in an urban area has all sorts of practical problems. Also they become dependant on the electronics for disconnecting on practically any fault to earth, and if it fails they are in a worse position than TN-C-S as only one earth rod of fairly high impedance (hundred-ish ohms probably).
  • TN-C-S offers the reliable disconnect on OCPD operation (just like TN-S) and so no modifications to most existing installations that going TT would demand, and saves the DNO money.
It is not hard to see why we got here!

As it stands the regs on caravan supplies have basically forced TT use there for some time now, but that is a small proportion of installs. Only now are the rapid rise in EV use is focusing attention on the risks of open-PEN faults once more.
 
And on that very topic I found this paper interesting:
(source https://myenergi.com/wp-content/uploads/2019/09/Protection-against-damaged-PEN-Conductor-r1_0.pdf )

The number of reported open PEN faults is higher than I'd have guessed (and I can't help imagine there are plenty not reported)

1615317072177.png

The paper also goes on to discuss 3 pole automatic switch based upon RCD principles by measuring the earth fault current, with a focus on EV charging points and the inherent dangers on TN-C-S with broken PEN conductor.
 
I suspect the move to TN-C-S was started many years ago when (a) most folk did not have significant outdoor power requirements like EV and hot-tubs, and (b) when the cables going in were nice and new and joint failures of the outer PEN of aluminium waveform cables was not an expected thing.

Fast-forward 30 odd years and here we are.
  • Proper TN-S would be the safest/best system, but costs the DNO that earth extra conductor.
  • Going TT like much of the EU avoids the DNO expense and the open-PEN risk. But in turn it pushes the extra cost on the home owner as they need an incoming RCD (unusual over two decades ago before the regs demanded them on most circuits) and an earth rod, which in an urban area has all sorts of practical problems. Also they become dependant on the electronics for disconnecting on practically any fault to earth, and if it fails they are in a worse position than TN-C-S as only one earth rod of fairly high impedance (hundred-ish ohms probably).
  • TN-C-S offers the reliable disconnect on OCPD operation (just like TN-S) and so no modifications to most existing installations that going TT would demand, and saves the DNO money.
It is not hard to see why we got here!

As it stands the regs on caravan supplies have basically forced TT use there for some time now, but that is a small proportion of installs. Only now are the rapid rise in EV use is focusing attention on the risks of open-PEN faults once more.

1 vote here for PROPER mantained TNS
 
The number of reported open PEN faults is higher than I'd have guessed (and I can't help imagine there are plenty not reported)
I think they will all be reported.

The DNOs have that duty, and the huge voltage swings and possible damage to home owner's equipment makes it hard for the home owners to ignore/not report and have fixed!
 
I have always thought regulation 722.411.4.1 (iv) where protection from a PEN fault is by measuring the utilization voltage between L & N and then disconnecting all conductors if it is outside the range of 207v - 253v, as a bit of a cop-out and only really solving half the problem as it is possible to have a PEN fault and the voltage to remain within that range

I have been thinking however the as a PEN conductor has multiple electrodes along its length so a break in the PEN conductor should still ensure you are connected to one or more electrodes, but I guess the weakest points are the joints and in particular the joints where individual houses etc connect to the PEN conductor, So would it be the case that most PEN faults occur at a joint where it branches off to feed a house also the section to the house is very unlikely to have any electrodes on, but in this case as it is only one house affected the above 722.411.4.1(iv) would work in most cases (subject to extraneous parts which are bonded), so is this why it is accepted as a way to mitigate PEN faults as in most cases it will protect due to the above

Attached is a crap picture to show the joints I am trying to convey
 

Attachments

  • IMG_20210309_200400201.jpg
    349.4 KB · Views: 13
the weakest points are the joints and in particular the joints where individual houses etc connect to the PEN conductor
I know exactly what you are saying, and I have no experience with the public distribution side but I wonder if it is three conductors coming together at that joint location in a resin joint, and a joint failure would also sever the ongoing PEN to the next joint.
On large private estates I've seen it done like this (and had to fix it after a mini-digger driver had a bad day!).
 
50 or so houses were affected where my Son was living a few years ago, spread across all 3 phases.
It was a newish estate of around 50 or so houses and the Neutral connection failed where the estate was connected to the existing cable in the main road.
It cost Western Power tens of thousands to sort out the damage caused.
 

Reply to Lost neutral on PME consequences in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K
Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth...
Replies
3
Views
541
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
504
https://ibb.co/qRhctQk Came across this setup today, upon further investigation i noticed the distributors neutral terminal completly slackened...
Replies
35
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock