Hi all

question regarding grouping factors in a domestic house. is there still a need to apply grouping factor Calcs in a 3 bed domestic house hold, I mean do we apply grouping factors for going through joist holes,where there is say 9 cables going through a 32mm hole but length of grouping at a length of 100mm. Is the calcs required or is it just judgement where cables through a hole and still plenty of moving is acceptable ? Thanks in advance
 
Amount sounds about right in 32mm hole,it’s pretty conventional circiuts were talking about here.
No different to conduit cabling say in 20 mm .
There will always be another hole drilled if required,so grouping can be done in a efficient way.
 
In an average domestic installation the conductors will rarely, if ever, reach any sort of meaningful operating temperature. As such I would not feel the need to apply rating factors for cables in this instance.

Caveat: I would assess this on each installation and intended use. If someone in the future decided to do lots of growing in the property then grouping would have to be reassessed.
 
Hi lads

thanks for the replies,yeah that is what I would think that domestic cables are not all fully loaded prob never will get up to full load so grouping factor in this situation won’t need to be applied.More for commercial and industrial situations ? Cheers
 
Hi lads

thanks for the replies,yeah that is what I would think that domestic cables are not all fully loaded prob never will get up to full load so grouping factor in this situation won’t need to be applied.More for commercial and industrial situations ? Cheers

No, the assessment of grouping is for all situations.
It's not a case of 'probably never get up to full load' or not assessing the grouping of cables.
It is just that the assessed use of the cables will be under the 30% stated in the regulations.
 
Ok ?. also some of the cables are going through engineering joists, where it’s about about a 10mm board. Will the grouping factors through these holes really matter in this installation purpose as the distance is so small plus i have counted nine circuits through a 32mm hole ?
 
No, the assessment of grouping is for all situations.
It's not a case of 'probably never get up to full load' or not assessing the grouping of cables.
It is just that the assessed use of the cables will be under the 30% stated in the regulations.
That's 30% of the grouped rating Of each cable,not the the flc of said cable.
Regards,S
 

Reply to Grouping factors domestic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
918
Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
891
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock