Bungalow, existing property, owner occupied. Front door opens into hallway. Kitchen is separated from the hallway by a door. Kitchen also has a external door leading to garden.

If installing to minimum building regs requirements (Grade D2 Category LD3), does the kitchen need a heat alarm?

My old building regs book shows a diagram that suggests no heat alarm needed in the kitchen (the kitchen in said diagram has an external door), but it's 17th edition so a bit outdated.
 
Just put one in if you can.

The basic coverage I believe (without checking) is hall, landing and kitchen because it’s a high risk
 
LD3 states alarms in circulation spaces that form part of escape routes,this includes loft conversion,landing and hall only.

we usually install to LD2 which includes high risk and the principle habitable room as well as LD3.
 
I would always put a heat in an internal garage with room above too
 
LD3 states alarms in circulation spaces that form part of escape routes,this includes loft conversion,landing and hall only.

we usually install to LD2 which includes high risk and the principle habitable room as well as LD3.
THIS

As a bare minimum for domestic homes you need a linked smoke up in the loft ( if its a habitable room ) , landings / stairwell and entrance hall

On a full re-wire I will always aim to get a heat in the kitchen but its not essential
 
This is the problem when a customer knows a little too much.

They will have been told that it’s not needed, which it isn’t according to the standards, but if you suggest it’s a good idea to have one, they think you’re just trying to rip them off with unnecessary work.

I’m glad I work in Scotland. They’ve standardised every home, owned or rented, to a minimum level that exceeds LD3
 
LD3 states alarms in circulation spaces that form part of escape routes,this includes loft conversion,landing and hall only.

we usually install to LD2 which includes high risk and the principle habitable room as well as LD3.
Would the kitchen not be considered to be this, having the back door to the property in it?
 
Yes, it's easier in Scotland, for sure. I usually install to LD2, with a wee bit of "extra" LD3 in there if there are numerous possible "escape routes". However, in a recent job there were 4 possible escape routes and I agreed with the client to cover 2 of those, front and back, as the likelihood of escape being barred was negligible.
 
Spot on #7.... Its part of the escape route to back door
 
Heat alarm in kitchen? Always! Part of escape route...definitely!
 
  • Like
Reactions: Pretty Mouth
The latest BS5839 - for an existing owner-occupied bungalow, recommends Grade F2 LD3 as minimum - and says they normally "need to be interlinked".

As already mentioned, Grade LD3 is defined as "a system incorporating detectors in all circulation areas that form part of the escape routes from the premises."

It seems that a kitchen doesn't count as a "circulation area", even if it is on an escape route from the premises.

From the book - "circulation area : area or space (including a stairway) used mainly as a means of access between a room and an exit from the building or compartment"

It also states that "(i.e. heat detectors should not be used in any Category LD3 system)"

So technically it would not be needed to meet the minimum standard as defined by the new BS 5839, which I guess is the most recent relevant document and would be the one Building Regs cross reference.

Doesn't mean it's not a bad idea, of course.
 
  • Like
Reactions: Pretty Mouth
Bungalow, existing property, owner occupied. Front door opens into hallway. Kitchen is separated from the hallway by a door. Kitchen also has a external door leading to garden.

If installing to minimum building regs requirements (Grade D2 Category LD3), does the kitchen need a heat alarm?

My old building regs book shows a diagram that suggests no heat alarm needed in the kitchen (the kitchen in said diagram has an external door), but it's 17th edition so a bit outdated.
just bang a heat in there as long as it is 500mm from the wall its ok and your room is no longer than 5m if its your house then you can do what you want if your living in it or just ask the fire brigade they give away free wireless fire angel devices now,or do what ive done and put a proper fire alarm in your house ....no more wafting the detector with a t-towel i just silence it
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwickshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Heat alarm needed in kitchen?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Pretty Mouth,
Last reply from
skidmark,
Replies
11
Views
1,772

Advert