Bungalow, existing property, owner occupied. Front door opens into hallway. Kitchen is separated from the hallway by a door. Kitchen also has a external door leading to garden.

If installing to minimum building regs requirements (Grade D2 Category LD3), does the kitchen need a heat alarm?

My old building regs book shows a diagram that suggests no heat alarm needed in the kitchen (the kitchen in said diagram has an external door), but it's 17th edition so a bit outdated.
 
LD3 states alarms in circulation spaces that form part of escape routes,this includes loft conversion,landing and hall only.

we usually install to LD2 which includes high risk and the principle habitable room as well as LD3.
THIS

As a bare minimum for domestic homes you need a linked smoke up in the loft ( if its a habitable room ) , landings / stairwell and entrance hall

On a full re-wire I will always aim to get a heat in the kitchen but its not essential
 
This is the problem when a customer knows a little too much.

They will have been told that it’s not needed, which it isn’t according to the standards, but if you suggest it’s a good idea to have one, they think you’re just trying to rip them off with unnecessary work.

I’m glad I work in Scotland. They’ve standardised every home, owned or rented, to a minimum level that exceeds LD3
 
Yes, it's easier in Scotland, for sure. I usually install to LD2, with a wee bit of "extra" LD3 in there if there are numerous possible "escape routes". However, in a recent job there were 4 possible escape routes and I agreed with the client to cover 2 of those, front and back, as the likelihood of escape being barred was negligible.
 
The latest BS5839 - for an existing owner-occupied bungalow, recommends Grade F2 LD3 as minimum - and says they normally "need to be interlinked".

As already mentioned, Grade LD3 is defined as "a system incorporating detectors in all circulation areas that form part of the escape routes from the premises."

It seems that a kitchen doesn't count as a "circulation area", even if it is on an escape route from the premises.

From the book - "circulation area : area or space (including a stairway) used mainly as a means of access between a room and an exit from the building or compartment"

It also states that "(i.e. heat detectors should not be used in any Category LD3 system)"

So technically it would not be needed to meet the minimum standard as defined by the new BS 5839, which I guess is the most recent relevant document and would be the one Building Regs cross reference.

Doesn't mean it's not a bad idea, of course.
 
Bungalow, existing property, owner occupied. Front door opens into hallway. Kitchen is separated from the hallway by a door. Kitchen also has a external door leading to garden.

If installing to minimum building regs requirements (Grade D2 Category LD3), does the kitchen need a heat alarm?

My old building regs book shows a diagram that suggests no heat alarm needed in the kitchen (the kitchen in said diagram has an external door), but it's 17th edition so a bit outdated.
just bang a heat in there as long as it is 500mm from the wall its ok and your room is no longer than 5m if its your house then you can do what you want if your living in it or just ask the fire brigade they give away free wireless fire angel devices now,or do what ive done and put a proper fire alarm in your house ....no more wafting the detector with a t-towel i just silence it
 

Reply to Heat alarm needed in kitchen? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
300
Hello, in preparation for renting out our home we have requested an Electrical Certificate and our electrician is doing a few minor tidy up jobs...
Replies
6
Views
858
Hi guys. I am wiring a kitchen extension and planning to install seprate CU for this. I have two questions if you guys help me finding answers...
Replies
4
Views
3K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock