Hi guys, as some of you might know I`m new to the NIC DI scheme and new to filling out these purple certs.

Q1. On the EIC purple certs, under the "SUPPLY CHARACTERISTICS" section, it asks for the external earth fault loop impedance by enquiry. Does anyone actually enquire or what reading should I put in there?

Q2. Same question as above but regarding the two nominal voltage readings?

Q3. What to fill in by the "ELECTRODE RESISTANCE" box?

Q4. Main switch voltage rating.......do you put the highest or lowest or both?

Thanks Guys
 
These are pretty much guesses as I'm not with NIC (Yet)
Q1 I never enquire, I always measure it. Is there another box on there for a measured Ze? If not I'd think it would be perfectly acceptable to put measured instead of enquired
Q2 If its a 3phase the entry is going to be 230/400.
Q3 Only applicable if there is an earth electrode not applicable unless its a TT
Q4 How do you mean by both voltage ratings? Shouldn't there be just one?
 
Either 0.35 tn-cs or 0.80 tn-s or measured Ze tt or just put in measured Ze (NIC) guy told me it didn't really matter which.
Nominal voltage Uo 230 other box only applicable if 3 phase then 415
Electrode resistance only applicable if tt installation if not then N/A
Mainswitch voltage rating written on switch.
 
Hi guys, as some of you might know I`m new to the NIC DI scheme and new to filling out these purple certs.

Q1. On the EIC purple certs, under the "SUPPLY CHARACTERISTICS" section, it asks for the external earth fault loop impedance by enquiry. Does anyone actually enquire or what reading should I put in there? ​ Ordinarily your measured value of Ze would go in here. There are occasions where the measurement of Ze isn't possible due to not being able to shut the supply off for example. Then you use the value obtained by inquiry to the DNO.

Q2. Same question as above but regarding the two nominal voltage readings? The U value is only applicable on a 3P installation as it is the nominal voltage between lines, and is 400V. The Uo value is the nominal voltage between line & earth and is 230V

Q3. What to fill in by the "ELECTRODE RESISTANCE" box? If you are working on a TT system with an earth electrode, the measured resistance of the electrode goes here. If not a TT system N/A.

Q4. Main switch voltage rating.......do you put the highest or lowest or both? The highest rating marked on the switch i.e 230V or 400V etc.

Thanks Guys

My replies in blue.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Help with filling out NIC certs please?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Ross1,
Last reply from
Guest123,
Replies
4
Views
3,258

Advert