L

londonlec

I have some remedial works to do on a fairly large commercial installation.
The majority of the submains from the main panels are protected by 63 and 100A MCCBs, and as a results of a high Ze (0.24), a lot of the submains Zs’s don’t meet the regs figure.
Replacing the cables is not an option, and won’t reduce the Zs down enough anyway.
So I was going to refeed the affected circuits via BS1361/BS88 fuses, which have a much higher (almost double) permitted Zs.
Does anyone else have any better ideas?!
Many thanks in advance.
 
What make of MCCB are they? the Max Zs vary with different makes 100 amp Square D max zs is 0.36 with out applying rule of thumb, what are the max demands of the submains, Some MCCBS can be turn down to 80 % of the current value which may get you inside the disconnection time.
 
What's the incomer rating and type of earthing? For a supply with lots of 63A & 100A subs a PFC of 1kA seems rather wimpy. Is that Ze definitely accurate?
 
decimal point error perhaps.................or maybes 2 depending where taken from:)

My main board shows pfc as 24 zillion amps.................well it is only 50 paces from our trannie:)
And I mean tx before we go off on another tangent!!!

All I said was soggy mars bar and we have war and peace elsewhere fgs lol
 
I have some remedial works to do on a fairly large commercial installation.
The majority of the submains from the main panels are protected by 63 and 100A MCCBs, and as a results of a high Ze (0.24), a lot of the submains Zs’s don’t meet the regs figure.
Replacing the cables is not an option, and won’t reduce the Zs down enough anyway.
So I was going to refeed the affected circuits via BS1361/BS88 fuses, which have a much higher (almost double) permitted Zs.
Does anyone else have any better ideas?!
Many thanks in advance.

Do you actually know the max Zs of these MCCB's, as every manufacturers figures differ, even between model numbers for a given rating from the same manufacturer??

Check before even contemplating changing out, or backing up with HRC fuses!!
 
Thanks for replies. Yes the MCCBs are Merlin Gerin NSX type (from memory), I cannot adjust them down as 1. they are operating at near full current, and 2. according to Merlin the Max Zs is the same regardless of adjustment (as someone has said). I make the Max Zs for these breakers as 0.24. The measured Zs is 0.46.
 

Reply to High measured Zs values in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. I got hands to a EMF meter (emf-390 v2). I walked around in our house and noticed almost everywhere high electrical fields of 50v/m+. I have...
Replies
3
Views
968
I am helping a local football club who are having some issues with Zs being too high on the submain. They have the supply Henley blocked into a...
Replies
9
Views
2K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Hi everyone, Consider we have an RCD+MCB protection for a circuit. if we follow the tables for Zs values of a 10A, MCB, type C, the maximum value...
Replies
6
Views
2K
D
Given that Amd3 reduced max Zs values slightly what is everyone coding if a measured reading falls between the pre Amd3 value and the post Amd3...
Replies
73
Views
10K
Deleted member 9648
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock