Hi everyone,
Consider we have an RCD+MCB protection for a circuit.
if we follow the tables for Zs values of a 10A, MCB, type C, the maximum value shall be 1.75 Ohm, this happens when 100A current flows ( as per MCB breaking curve). When the RCD disconnects the circuit in much less current, why do we still need to measure and verify Zs values?! RCD will never allow the current to reach some where near 100A! so even if the Zs value is much higher than permitted, it does not matter because the RCD will remove the fault. Am I wrong?!
 
both right and wrong. RCD will disconnect at approx 30mA, but it means that you are relying on a RCD for fault protection, whereas they are meant to be additional protection. fault protection should be provided by the MCB.
 
  • Like
Reactions: DPG
both right and wrong. RCD will disconnect at approx 30mA, but it means that you are relying on a RCD for fault protection, whereas they are meant to be additional protection. fault protection should be provided by the MCB.
Thank you. Dont see the problem on relying on the RCD though but you are right, as per regulation, it shall be used as additional protection.
 
What would happen if the RCD became faulty?
 
That’s why we test rcd’s.
It’s a non argument to say such a thing as what if the rcd becomes faulty.
If you worried about that then what’s the point of installing one?
How do we know that an mcb is not faulty?
Tho primarily used for additional protection a 30mA rcd will give fault protection also for say TT domestic installations and any other type of installation
 
Last edited by a moderator:
What would happen if the RCD became faulty?
I guess we can ask this question for all protective devices. plus, testing RCD is one of the testing procedures that we do as per BS7671 during routine checks and periodic inspections. I guess by having the RCD, even if the Zs values are slightly higher, everything is still protected by good margin.
 
Also the RCD will not detect or disconnect a live -neutral fault .
only the MCB can do this if enough current flows
 
  • Like
Reactions: static zap

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dubai, UAE
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
All Other Countries (This Is English Speaking Website Only - WE don't mind Google Translate Users :)
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Zs values when there is additional RCD protection
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
arashabb,
Last reply from
newfutile,
Replies
6
Views
2,060

Advert