I've been on this job to do an inspection before fitting a new RCD OR RCBO board. In most of my career until now the CPC is inside the T+E cable. This property has a separate CPC all through out the building. Only where there has been modifications, modern wiring has been used. If I can prove the ZS is good, is it ok to connect to this system. It's seems to be mainly the lighting that is wired in single sheathed cable which has been ran in conduit. I am hoping if anyone has any information regarding the regs about separate bare earth running through the property. There is a risk of borrowed neutrals if changing to an rcd or rcbo board. The customer does not want a Rewire but wants spots fitted and sockets moving. I have convinced him to change the board, now I am worried about nuisance tripping. However if you could advice about the earth mainly would be a great help. Personally I feel the wiring was good for it's day.

IMG_20181017_102010958.jpg
 
Sticking my neck out here I’d say of course Because regs are not retrospective as long as all the tests are good and you comply with the current regs regarding RCDs etc I don’t really see it as any different to connecting to Red and black PVC.
 
Last edited:
  • Like
Reactions: sham
Where does the earth originate ? In my experience separate bare cpcs like this are often connected to lead water pipes as a means of earthing.
Never actually seen that but good point. As long as the earth does actually come from the CU/fusebox and not the water pipe and all of the tests are ok I don’t see a problem.

Obviously upgrading the bonding as well when replacing the board
 
Never actually seen that but good point. Obviously upgrading the bonding when replacing the board

Seen it most where rubber twin (no cpc) was used, either VIR twin or TRS. Bare cpc was often taken from a lead pipe, either soldered on or clamped on, and taken individually to sockets.
 
  • Like
Reactions: MFS Electrical
It appears to be connected to the earth on the board which is fed by TN-S
I’d be looking to just confirm that but I really don’t think there’s a problem...
 
Seen it most where rubber twin (no cpc) was used, either VIR twin or TRS. Bare cpc was often taken from a lead pipe, either soldered on or clamped on, and taken individually to sockets.
Found this in the ceiling also was interfering just with my continuity test, traced the wire back to this . 1mm cable connected and two lead cables of 2.5. It was a stressful day lifting floor boards.

IMG_20181017_100309007.jpg
 
Found this in the ceiling also was interfering just with my continuity test, traced the wire back to this . 1mm cable connected and two lead cables of 2.5. It was a stressful day lifting floor boards.

View attachment 44941
Is that the guts of an old thorn 8ft brings me back to the first few months of my apprenticeship taking down these old lumps and replacing them with 6fts and I mean lumps just about a 2 man lift to get the bloody thing down:screamcat:
 
Because there are bare earthed in the board I have come to that conclusion, but to no for sure, there are so many limitations
Are the main gas and water bonded?
 
  • Like
Reactions: sham
It appears to be connected to the earth on the board which is fed by TN-S
Time gone by, bare earth was used for bonding services, and used as main earth lead.
 
Is that the guts of an old thorn 8ft brings me back to the first few months of my apprenticeship taking down these old lumps and replacing them with 6fts and I mean lumps just about a 2 man lift to get the bloody thing down:screamcat:
Well, this is under the upstairs floor board and two cables come out, they felt cold and are metal, never seen anything like it. These metal cables go to the end of a roof end, loft. (It is a bungalow) they end up in junction boxes that go nowhere else. Diconnected
 
I’d disconnect the bonding and the bare earths from the board and do an R2 on the bare earth from the end at the board to ensure its complete and then again at the bit your going to connect into and to the board itself and then the pipes themselves just to rule out that the bare earth was coming from elsewhere I reckon if you do that you’ve pretty much proved beyond reasonable doubt that the earth is suitable and actually coming from the CU and not the pipes or anywhere else.
 
  • Agree
Reactions: Bob Geldoff1234
Well, this is under the upstairs floor board and two cables come out, they felt cold and are metal, never seen anything like it. These metal cables go to the end of a roof end, loft. (It is a bungalow) they end up in junction boxes that go nowhere else. Diconnected
Old lead cables probably wonderful stuff :rolleyes: the rest of the cables in the house aren’t lead are they?
 
The water pipe by sink is bonded to the Earth bar but not to main stop tap. Nobody knows where stopcock is inside.
The Gas, I will investigate tommorrow, but boiler is cross bonded
I’m just wondering if the bare earth leaves the board swings by the pipes and then on to the circuits
 
Seen it most where rubber twin (no cpc) was used, either VIR twin or TRS. Bare cpc was often taken from a lead pipe, either soldered on or clamped on, and taken individually to sockets.
What the h**l is TRS by the way?
 
  • Like
Reactions: sham

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
WEST MIDLANDS

Thread Information

Title
I'm not sure if the Regs allowed separately bare earths.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
111

Advert

Thread statistics

Created
sham,
Last reply from
MDJ,
Replies
111
Views
10,238

Advert