Hi all,

Just a quickie. I carried out an insulation resistance test on a lighting circuit which only has two rooms consisting of 4 lights.

Live to earth and neutral to earth was fine but when I tested live to neutral I got a short circuit.

All the bulbs were removed so just wondering if anyone had any ideas?

The Zs reading was 0.73 ohms.

Thanks
 
If this was an existing circuit and it wasn't tripping or blowing fuses before you arrived then there's some kind of load still connected to it. Check the L-N resistance with a normal multimeter and try figure out what is connected and where.
 
Hi all,

Just a quickie. I carried out an insulation resistance test on a lighting circuit which only has two rooms consisting of 4 lights.

Live to earth and neutral to earth was fine but when I tested live to neutral I got a short circuit.

All the bulbs were removed so just wondering if anyone had any ideas?

The Zs reading was 0.73 ohms.

Thanks

Two possibilities-:

1.Something still connected which may or may not now be fried....(tv booster in loft....loft light)?
2. A fault.
 
There are no neons on the switches.

There is a tv amp in the attic, would that be spurred from lighting by any chance?
They often are, try unplugging it and retesting. If it clears then there's your problem, hopefully you won't have fried it. This is an example of why it's wise to do a test on 250v before the proper one at 500, they don't like it up em
 
For all it takes its wise to do a quick continuity test between L & N before applying 500V.

Edit. Or as Trev states IR test at 250V
 
Last edited:
I'm pretty sure it's the tv booster!

Will check it out tomorrow as its a property I have just purchased to rent out. Therefore, no rush whilst its unoccupied.

Cheers for all the advice :)
 
I'm pretty sure it's the tv booster!

Will check it out tomorrow as its a property I have just purchased to rent out. Therefore, no rush whilst its unoccupied.

Cheers for all the advice :)

You may need to buy yourself a new amp

Every day is a learning day - but I really don't know what possesses people to do a 500V IR test on a system which they are not 100% familiar with
 
if they're short try pulling a bit of slack through. :75:
 
You may need to buy yourself a new amp

Every day is a learning day - but I really don't know what possesses people to do a 500V IR test on a system which they are not 100% familiar with

I struggle to understand why people have test equipment when they can't understand test results it gives them.
 
Hi all,

Just a quickie. I carried out an insulation resistance test on a lighting circuit which only has two rooms consisting of 4 lights.

Live to earth and neutral to earth was fine but when I tested live to neutral I got a short circuit.

All the bulbs were removed so just wondering if anyone had any ideas?

The Zs reading was 0.73 ohms.

Thanks


It's those daffodils you're using in the lighting circuits mate.
 
if there was a short circuit between a phase conductor and neutral...either a protective device should have tripped or operated ...or you would have had something go...BANG !!!
 

Reply to Insulation Resistance - Live to Neutral short in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in...
Replies
12
Views
1K
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
646
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
575
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
720

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top