Inapplicable could apply to all of the test results for out going circuits when conducting a CU change.
Not all of them as you need to verify that you've correctly reconnected them and that ADS will operate. Certainly some of it may not be applicable though.
As above. Circuit protection is often altered in these upgrades. (3036 to 60898 OCPD's for example) so to confirm ADS, Zs would have to be taken and recorded as a minimum. Additional protection by RCD may well have been added too and these would also need testing and recording to prove satisfactory.
If you’re changing from BS 6036 to BS EN 60898, then you should be checking Zs beforehand, especially now we have Cmin.
Yes, if you’ve installed RCDs, they will need testing, because it’s part of the work you have done.
Reply to IR testing on CU upgrade in the UK Electrical Forum area at ElectriciansForums.net
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
I had just installed a heat alarm on the downstairs lighting circuit during a kitchen rewire. The new kitchen ring / cooker circuit I tested IR...