Discuss What's common practice with IR tests on lighting circuits? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
I had just installed a heat alarm on the downstairs lighting circuit during a kitchen rewire.

The new kitchen ring / cooker circuit I tested IR for L-N and N-E at 500v, fine, but the DS lighting circuit consisted solely of 21 LED downlights, in various rooms and the alarm. All of which say do not IR/

How do you take results when this happens? or what do you fill out the EIC IR columns with? or do you not generally bother?
 
Insulation resistance testing must be carried out on all new wiring, between live conductors, between line and earth, and between neutral and earth. The test voltage should be 500V.

The testing would be carried out as the wiring is installed, not just at the end when all the lights, USB sockets, smoke alarms etc have been fitted.

Finally, after all the equipment has been fitted, an insulation resistance test should be carried out between line and neutral connected together, and earth. The test voltage may be reduced to 250V.

All this information is in BS7671.
 
Insulation resistance testing must be carried out on all new wiring, between live conductors, between line and earth, and between neutral and earth. The test voltage should be 500V.

The testing would be carried out as the wiring is installed, not just at the end when all the lights, USB sockets, smoke alarms etc have been fitted.

Finally, after all the equipment has been fitted, an insulation resistance test should be carried out between line and neutral connected together, and earth. The test voltage may be reduced to 250V.

All this information is in BS7671.

Is there anything that may skew the readings e.g. LEDs, smoke detectors, WiFi etc. when doing the combined LN to earth.

Just done an EICR in a student house and it’s impossible to remove everything. Wiring is only 5 years old, but I’m getting a reading of 30M ohm.
 

Reply to What's common practice with IR tests on lighting circuits? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
622
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
609
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock