Discuss Ir tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
19
Just testing a 3 bed house i've re wired, its a empty property totaly gutted and re furbed Re plastered etc... Just doing my IR Tests on my rings and getting results around 129 meg at 500v nothing connected anywhere and no neons etc, Should i expect to be getting >500 as with all other curcuits ive tested?. Just seems odd to me these are lower than the rest
 
damp plaster? anyway 129Meg. is a well good reading. don't worry.
 
I always Con checked and IR tested the cable when it was new and still on the drum before i used it just to be on the safe side. Never found owt wrong, but never say never.
But i wouldnt worry, although you would expect the meter to go off the scale, 129 is still good, and as Tel says, probably damp.

Cheers............Howard
 
To the OP, you state a rewire..may I ask the test method you are using and where abouts you are placing your testing probes/croc clips in relation to the circuits in question ?

J
 
i would hope he's clipping to the bare ends of the stripped conductors.:D
 
yep. IR testing is for the circuit/s alone. should never IR test with RCDs or any other sensitive equipment connected.
 
i would hope he's clipping to the bare ends of the stripped conductors.:D


yep. IR testing is for the circuit/s alone. should never IR test with RCDs or any other sensitive equipment connected.




A bit tricky if your doing it by the book:


The insulation resistance measured with the test voltages indicated in Table 61 shall be considered satisfactory if the main switch board and each distribution circuit tested seperately, with all it's final circuits connected but with current using equipment disconnected, has an insulation resistance not less than the appropriate value given in table 61.
 
The problem with that is it's guidance, prior to everything being RCD'd or RCBO'd pretty much in a domestic you could on a new install IR from the new tails if it was all >200 no drama, if you got an iffy reading split the circuits up find the problem, not so easy now with the current set ups, the other thing of course is the regs cover all scope of works, many of which don't have any RCD protection !

J
 
It still remains that everything should be terminated before IR testing - so you couldn't go on the bare ends of stripped conductors.

Bearing in mind the regs have only just been ammended, you'ld think they'ld have altered the above regulation (sorry, 'guidance'), if it was a problem.

In the 2391 I went on the outgoing side of the RCD (i.e. the buzz bar) without any issues.

The problem you've got is, if you do as you(jimmyboy) and telectrix suggest, by testing each circuit seperately and disconnected from the CU, you could still have issues between circuits.

I'll just give you a very quick example so you know what I'm on about :

Conduit install, you IR test L-N on a socket radial, (disconnected from board) - 500v >299 M everything rosy.

Unknown to you, though, the 'line' conductor you've just tested is shorting out to the neutral of a lighting circuit (within the conduit).
It won't be picked up because you had the socket radial circuit's conductors out of the board.

The same thing can apply to CPCs - you IR test L-CPC with the conductors disconnected from the board - >299...........but what if the 'line' conductor has been snagged on some earthed metalwork somewhere - again, it's not gonna show up.

This is the reason you test with all conductors terminated.
If you have sensitive equipment in circuits, then, as the regs state, you have to compromise some of the testing, but the fact remains you should IR test as much of the installation in it's finished (terminated) condition as possible.
 
Well old school says split the ring in the middle and test no a big job but it pins it down so 12 sockets on a ring cut it to 6 then 3 now you know what area you are looking at plus if its the live that is showing a lower reading then its just the live you break at each socket
 
I've had a couple of issues with brand new MK sockets recently. IR's the circuit and results were lower than expected, split the circuit and pin point to faulty new socket:thumbsup
 
The same thing can apply to CPCs - you IR test L-CPC with the conductors disconnected from the board - >299...........but what if the 'line' conductor has been snagged on some earthed metalwork somewhere - again, it's not gonna show up.

Surely if the Line conductor was snagged on the CPC/Earthed metalwork there would be an extremely low reading due to the fact no insulation is between the conductors and they are forming a circuit!!!! Technicaly giving you a R1+R2 reading??
 

Reply to Ir tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
319
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock