Hi everyone
My Napit assessment is approaching and it would be nice to get some feedback for my planned work on my of my friends workshop.
There is already a consumer unit but its without RCD protection and thats on the shop floor.
My plan is to make two circuits one lighting 6A and one Ring final circuit 32A in the workshop . I would hopefully install 3 spotlights and for ring final circuit 4/5 sockets .
But instead of connecting both circuits to main consumer unit I am planning to install Sub DB in the workshop which is Axiom Metal 17th Edition Garage/Workshop Consumer Unit 3 Way - https://www.toolstation.com/axiom-metal-17th-edition-garageworkshop-consumer-unit/p36399.
As I will only be using 6A and 32 and leave the 16 as spare so shall I just use 6mm cable to connect SubDB with main DB as it has Iz of 47A and my potential current usage would be 38. Furthermore as the main DB does not have RCD protection so I decide to install subdb for workshop which would have RCD protection for my circuit but I would only be showing the I have installed two circuits and leave the subDB out for any hassle.
Any suggestions and positive feedback is appreciate. Thanks in advance guys
My Napit assessment is approaching and it would be nice to get some feedback for my planned work on my of my friends workshop.
There is already a consumer unit but its without RCD protection and thats on the shop floor.
My plan is to make two circuits one lighting 6A and one Ring final circuit 32A in the workshop . I would hopefully install 3 spotlights and for ring final circuit 4/5 sockets .
But instead of connecting both circuits to main consumer unit I am planning to install Sub DB in the workshop which is Axiom Metal 17th Edition Garage/Workshop Consumer Unit 3 Way - https://www.toolstation.com/axiom-metal-17th-edition-garageworkshop-consumer-unit/p36399.
As I will only be using 6A and 32 and leave the 16 as spare so shall I just use 6mm cable to connect SubDB with main DB as it has Iz of 47A and my potential current usage would be 38. Furthermore as the main DB does not have RCD protection so I decide to install subdb for workshop which would have RCD protection for my circuit but I would only be showing the I have installed two circuits and leave the subDB out for any hassle.
Any suggestions and positive feedback is appreciate. Thanks in advance guys