Hi,
Need a word of advice, how should I run supply to two metal sheds that are located about 20m away from the main DB. Should I run in SWA with 10mm bonding and as separate circuit to each shed or through sub-board adjacent to them? What IPX of switch and lighting should be, I'm expecting some condensation as the sheds seems sealed?
Mike
I believe you can have the SWA connected to the home earthing arrangements, in this case TNCS. At the shed consumer unit when terminating the SWA use a plastic compression gland only. This will then separate the SWA earthing from the shed earthing arrangements. As the shed is of metal construction TT earthing will be required.
I'm thinking of sub-DB that split into two 6A lighting circuits, 4mm2 cable. Earthing arangement is TNCS so ideally 10mm bond but have no experience with this, so I can TT with RCD protection.
If 4mm is your calculated cable, run this as a normal circuit from your internal dist board. However when terminated into you new dist board you will need to seperate the earth and all paths back to the PME system. Then install a earth rod and TT the new installation. Dont forget to use the correct RCD protection for tmyour circuits, and if neccessary bond the metallic sheds.
Reply to lighting in the metal shed in the UK Electrical Forum area at ElectriciansForums.net
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Hi, I'm running a 70ft underground UF cable in 3/4 inch PVC conduit to 2 sheds. The sheds are 3ft from each other. I'm just a DIYer enthusiast so...
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
5K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...