D

dave1064

I am wondering where the maximum values (0.8 and 0.35 ohms) come from. Why are they 0.8 and 0.35?

Any help would be greatly appreciated
 
they come from BS7671. same as a lot of other useful guff.
 
it may well be. 0.8Ω is the max. allowed value.
 
I am wondering where the maximum values (0.8 and 0.35 ohms) come from. Why are they 0.8 and 0.35?

Any help would be greatly appreciated

Have a think about how the distributors means of earth is supplied on each supply characteristic. Why do you think you may record a higher impedance on a TNS supply?
 
I know where they come from. I am just wondering why the maximum is 0.8 for a tns system. Why not 1ohm or anything else. What is the reason?
 
because someone in a suit with letters after his name formed a committee and those values were the average taken out of the hat.
 
A TNS (Terra Neutral Seperate) system will utilise the metallic sheath on the supply cable as a means of earth. During the event of a fault, the fault current will flow down the outside sheath of the supply cable through the ground, back to the suppliers source of earth.

A TNC-S (Terra Neutral Combined System) uses the neutral conductor as a means of earth. Again, in the event of a fault, the current will flow back to the supply transformer through the neutral conductor.

Overall, a TNCS system should and will boast a lower overall fault loop impedance as the neutal conductor is of far lower resistance (impedance in an AC circuit) than a lead sheath running underground back to the supply transformer.

Are you at college? Have you asked your tutor?
 
Im a 4th year apprentice due to sit my trade test in 2 weeks. So been studying etc. And the question was asked why it is 0.8. Just wondered how they came up with 0.8 ohms
 
Have a look at tel's reply - it was probably calculated as an average using lead resistivity values etc - you won't specifically need to know why it's 0.8 Ohms.

So long as you know that 0.8 Ohms is the maximum value allowed on a TNS system, and a Ze reading will generally be far lower. Try to understand the principle of Ohm's Law and why different earth types have different maximum values.

Good luck
 
it's also a fact that while TN-S sheath is earthed at the sunstation ( apart from contact with the ground) a TNC-S system has multiple earthing points along the length of the supply cable (protective multiple earthing, PME) and that will reduce the Ze as well.
 
haha, why are the keys smaller than my fingers. quite often get the next one to the one i want. same thing happened when i got married. got the ex instead of her younger sister .
 
it's also a fact that while TN-S sheath is earthed at the sunstation ( apart from contact with the ground) a TNC-S system has multiple earthing points along the length of the supply cable (protective multiple earthing, PME) and that will reduce the Ze as well.

In theory, the lead sheath of PILC cables should never come in direct contact with the ground there was a insulating/bedding material between the old network wave line armour and the lead sheath. It is generally the breakdown of that insulating material allowing corrosive soil types to degrade/corrode the lead sheathing. Best ask Tony what the make-up was of those older PILC Waveline cables were, he has far more experience with them than i!!

Like the PME distribution cables, the TN-S cables would gain supplementary earthing from installations via bonding cables and connections to steel frame buildings and the like. One reason why they used to rod at TN-S service heads during the 50's. But as you rightly say PME cables will also (in theory anyway) have it's PEN conductor physically connected to earth at several points along it's length.
 
Last edited by a moderator:
Cheers guys. I know it wont come up but was just curiousity. That was the only explanation I could give. Just thought there might have been more to it.
 

Reply to Maximum Ze value for TNS and TNCS System in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
872
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
944
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
994

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock