A TNS (Terra Neutral Seperate) system will utilise the metallic sheath on the supply cable as a means of earth. During the event of a fault, the fault current will flow down the outside sheath of the supply cable through the ground, back to the suppliers source of earth.
A TNC-S (Terra Neutral Combined System) uses the neutral conductor as a means of earth. Again, in the event of a fault, the current will flow back to the supply transformer through the neutral conductor.
Overall, a TNCS system should and will boast a lower overall fault loop impedance as the neutal conductor is of far lower resistance (impedance in an AC circuit) than a lead sheath running underground back to the supply transformer.
Are you at college? Have you asked your tutor?