Hi guys
Megaflow cylinder
The connections on it are 1 2 3
In the book for an s plan you use 1 and 2 as your cylinder stat
When you turn the programmer on the zone valve is not working and firing the boiler up.
If you open valve manually it works
Now i thought faulty cylinder stat so i done a continuity test between terminal 1 and 2 and nothing
Between 1 and 3 got continuity
So switched cable from 2 to 3 on stat and it seems to work
Anyone had a similar problem