Megaflow cylinder

The connections on it are 1 2 3

In the book for an s plan you use 1 and 2 as your cylinder stat

When you turn the programmer on the zone valve is not working and firing the boiler up.

If you open valve manually it works

Now i thought faulty cylinder stat so i done a continuity test between terminal 1 and 2 and nothing

Between 1 and 3 got continuity

So switched cable from 2 to 3 on stat and it seems to work

Anyone had a similar problem
 
Don't run it like that! 1 is the common, 2 is the N/C and 3 is the N/O, if you use 3 instead of 2 to open the 2 port valve you will be heating the mega flow continuously and past it's maximum working temperature.

Now having said that what have you tested and what results did you get?
Have you checked the overheat protection?
Have you checked the temperature the stat is set at?
Is the immersion heater on and so heating the the megaflow up so that it is already warm?
 
Got it

Use 2 like i did to start with

what happens is even tho you call for heat the valve will not shut until the cylinder loses hot water and starts filling up with cold

Duhhhhhh me silly
 
So are you trying to say that the valve does not open until you draw off some of the hot water?

May I ask how much experience you have of working on heating control systems?
 
Yes the valve does not open until you draw out hot water.

Im23 got a little bit experience.

Checked the stat temperature and set at 60degrees

Done a continuity test on the cylinder stat
 
Ok, so you have identified that the valve only opens once you have drawn off some of the hot water stored in the cylinder.

Now tell us how you expect the system to operate, and why you think the current operation is incorrect?
 

Reply to megaflow in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
605
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
932
I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
1K
1 - Major supply fault, details unknown. By time I get there DNO already put in genny and are digging up road. 2 - Reason for call, heating not...
Replies
4
Views
594
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock