Ok so I'm finishing off some questions for a mock exam and its come up with:

"Explain why an exposed-conductive part MUST be connected to the MET to facilitate ADS?"

But my understanding is that anything that automatically disconnects the supply is connected to the Line(MCB) or the Neutral Bar(RCD), not the main earth terminal, Can someone explain to me how this works and what I'm missing?

am I mistaking the MET for the Earth bar when its something else? I'm not sure

EDIT: I think I have clicked onto it?, Is it that the current would flow through the exposed part and to the MET which would trigger the RCD because it would detect that current wasn't following residually anymore?
 
Last edited:
Ok so I'm finishing off some questions for a mock exam and its come up with:

"Explain why an exposed-conductive part MUST be connected to the MET to facilitate ADS?"

But my understanding is that anything that automatically disconnects the supply is connected to the Line(MCB) or the Neutral Bar(RCD), not the main earth terminal, Can someone explain to me how this works and what I'm missing?

am I mistaking the MET for the Earth bar when its something else? I'm not sure
Think about the Earth Fault Loop (draw it out if you need to) and what would happen if a live conductor came into contact with an exposed-conductive part that wasn’t connected to the MET. Where would the fault current go, what would cause ADS to operate?
 
Maybe swap terms for tangible things.
And forget RCD's completely, assume there aren't any.

Imagine you had a metal class 1 desk lamp plugged in.
Why does the body need connecting to the MET?
 
but I take it the RCD wouldn't trip if it touched the lamps body and it wasn't earthed?
You are correct about that. But.... It can help to think that you have three levels of protection, with the following simplified definitions:
Basic Protection (make sure you can't touch anything live)
Fault Protection (protection for overload, short circuit, including line conductor touching exposed conductive part)
Additional Protection (RCDs to turn it off damn quick if current that goes out doesn't come back)

A question about ADS will generally be about Fault protection as that always has to be there. RCD's don't always (though increasingly are).
To add it isn't quite that simple in all circumstances (e.g. TT installations) but it's not a bad starting point IMHO.
 
You are correct about that. But.... It can help to think that you have three levels of protection, with the following simplified definitions:
Basic Protection (make sure you can't touch anything live)
Fault Protection (protection for overload, short circuit, including line conductor touching exposed conductive part)
Additional Protection (RCDs to turn it off damn quick if current that goes out doesn't come back)

A question about ADS will generally be about Fault protection as that always has to be there. RCD's don't always (though increasingly are).
To add it isn't quite that simple in all circumstances (e.g. TT installations) but it's not a bad starting point IMHO.
wow ok brilliant thanks very much, so I will answer this with:

"Exposed conductive parts must be connected to the MET to provide a return path for current under fault conditions, without this there will be no ADS/Fault protection"
 
"Exposed conductive parts must be connected to the MET to provide a return path for current under fault conditions, without this there will be no ADS/Fault protection"
That's certainly correct and not a bad answer. The final icing on cake would be to say that enough current needs to flow to operate the over-current protective device within the required disconnection time.
So the key concept is knowing how much current (or what the max Zs will be) will make the MCB trip or Fuse blow within the required time.
 
That's certainly correct and not a bad answer. The final icing on cake would be to say that enough current needs to flow to operate the over-current protective device within the required disconnection time.
So the key concept is knowing how much current (or what the max Zs will be) will make the MCB trip or Fuse blow within the required time.
again brilliant thanks
 

Reply to MET and ADS in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
723
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
319
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock