I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a first floor, with a driveway underneath (originally to get carts under for deliveries), with the consumer unit, meter, gas meter etc in a cupboard on the neighbouring building's wall under cover of the first floor.
The extension builder, who said he knew what he was doing installed 50mm corrugated ducting from the extension to the consumer unit approx 12 metres, a metre underground with the gas pipe on gravel, with sand over the top and tape, then buried. I thought okay, we just have to get the t+e through for the cooker (10mm), sockets (2X2.5mm) and lighting (1X1.5mm), may be tight but it was buried by the time i saw it...
Upon investigation and talking to a domestic sparky mate of mine, (I only have experience with manufacture of lab equipment panels), I believe i will have to run SWA through the trunking...
First off, will I get 10mm SWA , 2X2.5mm SWA and 1.5mm SWA through a single 50mm trunking???
Would I be better running 10mm SWA for the cooker from a 50A breaker and 6mm SWA on 45A breaker on existing consumer unit to a garage type consumer unit in the extension and splitting with an RCD to 2.5mm for the socket ring and 1.5mm for the lighting on 2 seperate MCBs, rather than messing around with 4 cables from the consumer unit?
What is the best way to get it through? One at a time, together, method?
From most stuff I have read, pull blue polyrope through with the wire, tie off rope on cable, lube cable , a person pushing and a person pulling, hope sweat and a few choice words.
Any advice much appreciated.
The extension builder, who said he knew what he was doing installed 50mm corrugated ducting from the extension to the consumer unit approx 12 metres, a metre underground with the gas pipe on gravel, with sand over the top and tape, then buried. I thought okay, we just have to get the t+e through for the cooker (10mm), sockets (2X2.5mm) and lighting (1X1.5mm), may be tight but it was buried by the time i saw it...
Upon investigation and talking to a domestic sparky mate of mine, (I only have experience with manufacture of lab equipment panels), I believe i will have to run SWA through the trunking...
First off, will I get 10mm SWA , 2X2.5mm SWA and 1.5mm SWA through a single 50mm trunking???
Would I be better running 10mm SWA for the cooker from a 50A breaker and 6mm SWA on 45A breaker on existing consumer unit to a garage type consumer unit in the extension and splitting with an RCD to 2.5mm for the socket ring and 1.5mm for the lighting on 2 seperate MCBs, rather than messing around with 4 cables from the consumer unit?
What is the best way to get it through? One at a time, together, method?
From most stuff I have read, pull blue polyrope through with the wire, tie off rope on cable, lube cable , a person pushing and a person pulling, hope sweat and a few choice words.
Any advice much appreciated.