Discuss No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net
I'm doing a low ohnms continuity test. I'malso, what continuity test are you doing
Neon on switch between L and N?
also, what continuity test are you doing?
What exactly do you mean by not getting a continuity reading? how low was the IR Test? cooker sockets is working also?Not getting a continuity reading on the cooker circuit. I'm doing I.r. test and its low between l. N. Any ideas what the issue could be.
The cooker sockets is working also.
I have mate. I'm not getting a reading. When I link line and neutral I get 0.10 ohmsWhat reading are you getting. You will only get a line to cpc reading if you have connected a link across them.
Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work
Sound mate.
So the means of fault protection wouldn't function then. Additional protection might. But issue needs solving.But everything fine apart from no continuity on the line earth at cooker.
Test cont between LN LE NE IR the same and publish the results,Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work
Sound mate.
Ah - as he said it was 'working' I assumed it wasn't initial which may have been the wrong conclusion.If this is an initial verification do not energise the circuit for a Zs until this is resolved.
Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.Zs won't be fine on the cooker circuit I bet.
So, what is the next step you will make?
Fear not it does get easier.Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.
Reply to No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net