Probably going over old ground here but I have assessment soon on this job, new consumer unit fitted completed R1+R2 test at light pendants all ok but two way light was found to have no cpc at light switches although does have earth at pendant what can i do for my assessment have read esc guidance notes and seen that can fit warning notice at consumer unit for this upstairs lighting circuit or do have to try and get cpc to these light switches and back to ceiling rose, all advice greatfully appreciated
 
IMHO you need to balance the regulations, the upheavel & cost to the customer and the safety of the customer.

The Electrical Safety Council leaflet covers the situations where there is no cpc on the lighting circuit thoroughly.

If the customer doesn't have any metal fittings or switches on the circuit I'd make a note on the EIC and stick the appropriate label on the CU.

Others may have conflicting ideas!
 
agreed with above - just make sure any switch drops that have no cpc are not shock risks- screws that are metal with a metal back box for example, or as Murdoch points out class one plate switches.

You can get white plastic switches with caps for the screws, these will satisfy, or nylon screws can be used (hard to find IMO).

If you're really lucky, there'll be no carpets above all the drops, the floor boards will be loose and the last installer used oval conduit that has bags of space in it.... in which case get your green and yellow out!
 
I would check the other light switches, but the lack of cpc is not a problem.

Solution - where there is no cpc make sure all accessories are class 2 - fit the warning label on cu - at the unearthed switch boxes replace fixing screws by nylon screws.
 

Reply to No cpc at light switches in the Australia area at ElectriciansForums.net

Similar Threads

Not the usual per-1966 sort of "no CPC in wiring issue" but plastic light switches in plastic back-boxes in trunking wired in singles. The lights...
Replies
3
Views
1K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
615
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
445
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock