Went to look at a job today, place is about 30years old and has Wylex rewirable fuse board (timber one at that), 16mm tails on a 60A fuse, 16mm main earth (on PME) and 10mm water bond. At some point over the years a oil fired boiler has been added to the central heating to go with the solid fuel stove that's in the front room. Oil tank is in the back garden and the boiler is in the garage. The garage however is not accessible through the house and instead has to be entered from either the front drive or back garden. Is the garage therefore classed as being outside of the equipotential zone? Reason for asking is due to the lack of bonding to the oil pipe, is there none because it's not required (due to being outside the equipotential zone) or because of laziness?
 
is the inter connecting pipe works entering the house at any point on the system..!!!!

if yes then bond is a must!
 
Is this oil line likely to introduce an earth potential to the building i.e extraneous conductive part???
 
If the garage is using the TNCS earthing the equipotential zone includes the garage, and main bonding has to meet the requirements for a TNCS system.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Oil bond.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Thread Tags

Tags Tags
oil

Advert

Thread statistics

Created
Dunc,
Last reply from
Deleted member 9648,
Replies
4
Views
1,630

Advert